    Smile Pressure Test



    I am just about to start my own company and have only really worked with R407c. Does any one have info on R410, i need to know what sort of running pressures and what pressure is used to test the system with

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pressure Test

    Do you have a safe handling certificate and if so your handbook should give you the legal required test pressures?

    Other than that I would suggest downloading some material from websites such as Daikin or Mitsubishi to gather more information.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Pressure Test

    Quote Originally Posted by Langdellt View Post
    I am just about to start my own company and have only really worked with R407c. Does any one have info on R410, i need to know what sort of running pressures and what pressure is used to test the system with

    Thanks
    Try useing a comparitor.
    Or use the charts on coolpack

    http://www.et.web.mek.dtu.dk/Coolpack/UK/download.html

    taz

  4. #4
    Join Date
    Mar 2007
    Location
    England
    Posts
    34
    Rep Power
    0

    Re: Pressure Test

    Quote Originally Posted by Langdellt View Post
    what pressure is used to test the system with
    I test a R410a system to 300psi/20bar for 24 hours with OFN

  5. #5
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Pressure Test

    .

    There is a pressure testing procedure laid down in a European Standard, EN 378. - Refrigeration Safety.

    It's in 4 parts and for pressure testing specifically, you need to read Part 2, though I recommend being familiar with it all.

    .

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Pressure Test

    Quote Originally Posted by Rotax100uk View Post
    I test a R410a system to 300psi/20bar for 24 hours with OFN
    300psig is not even sufficient for the HP control setting on an R22 system

    Daikin, and others, recommend that R410a systems are pressure tested to 40Barg (600psig)

  7. #7
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: Pressure Test

    isnt it 1.1 times operating pressure for leak testing?

  8. #8
    Join Date
    Mar 2007
    Location
    England
    Posts
    34
    Rep Power
    0

    Re: Pressure Test

    Sorry i got confused about the R410a pressures:-

    Correct figures are

    STRENGTH TEST - - 43 BAR for 15 seconds
    LEAKAGE TEST - - 33 BAR for 24 hours

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pressure Test

    If you refer to Toshiba, as an example, you will find their requirements a useful schedule to follow:-

    psi bar Period
    50 3.45 5 mins
    200 13.79 5 mins
    450 31.00 5 mins
    600 41.36 1 hour
    500 34.47 24 hours

    Do be aware that some manufacturers are not so confident of their isolation valves and require you to withdraw the refrigerant charge before strength/pressure testing. Read the instructions first.
    Brian - Newton Abbot, Devon, UK