    R134a Help!!



    Got a little test rig coldroom at work to train on.

    Supervisor asked me to do home work

    I got to find out what to set the HP and LP up at

    Would any one know? the refrigerant is 134a
    He told me to keep in mind its a pump down system


    Thanks



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: R134a Help!!

    I'd set the hp switch for 60-65c condensing temperatue, you will need to convert this to a pressure with a slide rule or pt chart.
    The lp setting would depend on the design temperature of the cold room and the type of compressor.
    For a recip comp, i'd set the cut out at 2 or 3psi for a scroll it would possibly be higher.
    For the cut in you need to convert the design temperature of the room e.g. 12c into a pressure with you slide rule pt chart and make the cut in a few psi lower, maybe 5 or 10 psi.
    What you want it a nice wide differential to stop short cycling with a high enough cut out that it doesn't go into a vacuum and a low enough cut in that it will cut back in. If the cut in is too high the tev can limit the suction pressure to below the cut in pressure and you unit won't start till the room is too warm. This is more of an issue with pumpdown cut out.

    Jon

  3. #3
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: R134a Help!!

    Quote Originally Posted by monkey spanners View Post
    I'd set the hp switch for 60-65c condensing temperatue, you will need to convert this to a pressure with a slide rule or pt chart.
    The lp setting would depend on the design temperature of the cold room and the type of compressor.
    For a recip comp, i'd set the cut out at 2 or 3psi for a scroll it would possibly be higher.
    For the cut in you need to convert the design temperature of the room e.g. 12c into a pressure with you slide rule pt chart and make the cut in a few psi lower, maybe 5 or 10 psi.
    What you want it a nice wide differential to stop short cycling with a high enough cut out that it doesn't go into a vacuum and a low enough cut in that it will cut back in. If the cut in is too high the tev can limit the suction pressure to below the cut in pressure and you unit won't start till the room is too warm. This is more of an issue with pumpdown cut out.

    Jon
    All quality info but you've put a monkey spanner in the works, Deano will never fit all that on the palm of his hand

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: R134a Help!!

    Quote Originally Posted by VRVIII View Post
    All quality info but you've put a monkey spanner in the works, Deano will never fit all that on the palm of his hand
    Get bigger hands Deano

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: R134a Help!!

    lots of space on the reverse side of a p/t chart

Similar Threads

  1. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 12:44 AM
  2. Clogged condenser leading to no gas on R134a systems?
    By runningonavac in forum Refrigerants
    Replies: 12
    Last Post: 01-09-2009, 10:52 PM
  3. r12 vs r134a minifridges (efficiency)
    By ziddey in forum Fundamentals
    Replies: 10
    Last Post: 25-06-2009, 06:26 AM
  4. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Replies: 0
    Last Post: 28-02-2005, 09:05 AM
  5. Replies: 5
    Last Post: 01-03-2004, 09:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •