    Eliwell Ewpc 961



    HI,I HAVE A ELIWELL UNIT WHICH IS CAUSING A FEW PROBLEMS ON A COMMERCIAL DISPLAY FRIDGE,BASICALLY THE COMPRESSOR WILL NOT RUN EVEN WHEN INDICATION LIGHT IS ON.YOU CAN HEAR RELAY CONTACTS CLICK BUT WHEN YOU GIVE CONTROLLER A GOOD WHACK THE COMP WILL RUN.I SUSPECT DODGY RELAY CONTACT BUT MAYBE SOMEONE OUT THERE KNOWS DIFFERENT,THANKS



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Eliwell Ewpc 961

    Quote Originally Posted by KCDOMAPPS View Post
    HI,I HAVE A ELIWELL UNIT WHICH IS CAUSING A FEW PROBLEMS ON A COMMERCIAL DISPLAY FRIDGE,BASICALLY THE COMPRESSOR WILL NOT RUN EVEN WHEN INDICATION LIGHT IS ON.YOU CAN HEAR RELAY CONTACTS CLICK BUT WHEN YOU GIVE CONTROLLER A GOOD WHACK THE COMP WILL RUN.I SUSPECT DODGY RELAY CONTACT BUT MAYBE SOMEONE OUT THERE KNOWS DIFFERENT,THANKS
    I would change the controller, the contacts on the relay seem to be burnt.
    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Nov 2006
    Location
    Ireland
    Age
    50
    Posts
    6
    Rep Power
    0

    Re: Eliwell Ewpc 961

    Hi.Just change it for peace of mind. you will probably get a call next week saying the same problem is back. Good luck.IF in doubt get it out.

  4. #4
    KCDOMAPPS's Avatar
    KCDOMAPPS Guest

    Re: Eliwell Ewpc 961

    THANKS GUYS,ALL I NEED TO KNOW NOW IS WHERE I CAN GET ONE AT SHORT NOTICE WITH A FAST TURNROUND.ANY IDEAS?

  5. #5
    Join Date
    Feb 2007
    Location
    Australia
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Eliwell Ewpc 961

    Hi
    If the compressor supply feed/current is being carried by the contacts within the controller it may be an idea to have the controller power up an external relay and take the supply feed for the compressor thru that relay. Therefore if the compressor draws high amps, greater than the rated current of the new wired in relay and burns the contacts out you can throw the cheap relay away and not have replace the more expensive controller.

    Peter.

  6. #6
    Join Date
    Dec 2006
    Location
    lost
    Age
    52
    Posts
    7
    Rep Power
    0

    Re: Eliwell Ewpc 961

    Get one fro Thermfrost Cryo 020 8655 7600 about £20 should sort you out.

  7. #7
    KCDOMAPPS's Avatar
    KCDOMAPPS Guest

    Re: Eliwell Ewpc 961

    Thanks Chaps Have Now Sorted The Situation,appreciate Your Help.