    Field settings



    G'day,
    I'm new to this forum, but i see some of you have good knowledge of daikin A/C units.

    I just had 2 daikin A/C units installed, and I'd like to know how to disable the thermostat from the indoor units.. I wish to use the thermostat on the controller, and not have the thermostat from the indoor units average with the thermostat on the controller.

    Model outdoor unit -- rzp145dv1
    Model indoor unit -- fdyp145dlv1

    Thanks



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Field settings

    Sorry M8,
    To do what you want, you have to go deep in to the engineering mode.
    If you don't know how to do it, then I suggest you get the installer/an engineer in to do it for you.

    There are too many variables you could mess up whilst being in the control's engineering mode.

  3. #3
    Vincentair's Avatar
    Vincentair Guest

    Re: Field settings

    ok,

    how do I enter this deep engineering mode???

    Do u have a link to that info ??

  4. #4
    Join Date
    Feb 2007
    Location
    australia
    Age
    66
    Posts
    9
    Rep Power
    0

    Re: Field settings

    give daikin tech suport a ring on 1300362438 [thats an ozzie number] give them your model nos an they should be able to help ya....

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Field settings

    Why do you want to disable the return air sensor? This is the way the equipment has been designed to operate by the manufacturers and 99.9% of all systems operate just fine in this way.


    What led you to believe that what you want to do will make the system operate any better??
    Last edited by frank; 15-02-2007 at 09:43 PM.

  6. #6
    Join Date
    Dec 2006
    Location
    London
    Posts
    32
    Rep Power
    0

    Re: Field settings

    if your problem is that the return air is not coming directly from the conditioned area then you can purchase an extended sensor with 5 or so meters of cable and a wall mounted box from your daikin supplier

  7. #7
    Vincentair's Avatar
    Vincentair Guest

    Re: Field settings

    Quote Originally Posted by adams? View Post
    if your problem is that the return air is not coming directly from the conditioned area then you can purchase an extended sensor with 5 or so meters of cable and a wall mounted box from your daikin supplier

    Yes thats correct the air intake is from a differant location. An extended sensor should do the trick.

    Any online stores that supply extended sensors ??

    Thanks.

  8. #8
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Field settings

    The extended sensor you need is known as KRC SO1, it has a 10m cable and you just need to disconnected the factory fitted sensor and replace it with the extended sensor. Also program the field setting 10-2-02 to disable the remote controller sensor.

  9. #9
    Vincentair's Avatar
    Vincentair Guest

    Re: Field settings

    ok thx guys

  10. #10
    Join Date
    Apr 2007
    Location
    Adelaide
    Age
    51
    Posts
    11
    Rep Power
    0

    Re: Field settings

    Can I ask how this went? Did you manage to change the sensor? What did you do and how was the support from Daikin... if you needed it?

  11. #11
    Join Date
    May 2009
    Location
    Queensland
    Age
    76
    Posts
    15
    Rep Power
    0

    Re: Field settings

    Hi, Vincentair
    Although I cannot help you with your query I would ask if you can help me. I am repairing the PCB from a RZP1450V1 outdoor unit. The PCB is identified as A1P [I think] and has the markings PC1014H-1D. There is a resistor RSP1 that connects to plug X100A on this PCB. On the PCB I am working on this resistor is open circuit. It is a radial mounted 5W power resistor. However the value is obscure, due to over heating, so if you could have a look on your PCB and post to me the value of RSP1 I would be appreciative. With thanks for your help.

    Regards, KH


    A 'pdf' file is attached to my post: 'Daikin Control Unit Repairs' and is from a similar unit that shows RSP1 as 'R1' connected to plug X100A

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Field settings

    Check the date, the thread is over 2 years old