25-07-2010, 04:34 PM #1
walk-in start-up (hot)
Im looking for some basic rules that should be applied to starting up a walk-in. How is the charge initially set until the box can reach temperature enough to properly adjust?
Thx in advance
-
25-07-2010, 05:35 PM #2
Re: walk-in start-up (hot)
What refrigerant, design temp, txv or cap?, tell us more about your system.
Depends a lot on system configuration, the desired room temp, and the ambient temp.
System may not have a problem coping with pull down, or it may have a mop txv, a cpr valve, or the evap fans may be cycled till the room temp is at an acceptable level so that the compressor isn't overloaded.
I would say you don't want to adjust anything till the room is at or near design temperature.
Jon
-
25-07-2010, 07:46 PM #3
-
25-07-2010, 08:03 PM #4
-
26-07-2010, 12:01 AM #5
Re: walk-in start-up (hot)
Its actually a wine room using a 1/2 hp copeland condenser, R22 with constant pressure expansion valve and pump down solenoid trying to maintain 55 degrees