    A strange problem



    Actually I am not an expert of refrigeration, but a new mechanical engineer of a company working on air conditioners,
    we have a problem in a mono split type air conditioner, which is old( I dont know how much old), it is being used just for cooling in a measurement department of a factory. its problem:
    in summer, it has no problem but in winter, when it is powered on, in 30 sec gives "low pressure error". If it doesn't give an error, it works normally. An inverter kit had been installed to solve the problem but it hasn't... Even if condenser fan doesn t rotate, the error occurs, I think there is too much condensation. Some people think here that we should heat the lliquid tank or change the expansion valve, but it seems to be working normally.. waitng for your suggestions.. thx..



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: A strange problem

    Within 30 sec.?
    First, it would at least need a crankcase heater.
    Secondly, it would not have had time to reach a stable running condition after only half a minute - you could fit a timer that "shortens out" the LP switch for the first 3-5 minutes of the compressor starting.
    BUT.......
    A fridge guy (or A/C engineer) should put his gauges on it and then be able to tell you exactly what happens and what has to be done.




  3. #3
    Join Date
    Dec 2006
    Location
    London
    Posts
    32
    Rep Power
    0

    Re: A strange problem

    i agree with viking, get some gauges on. possibly also check lp controls - could also be faulty

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: A strange problem

    Could be a sticky 4 way valve.

    Needs a tech to put some guages on it though.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Nov 2006
    Location
    veghel
    Age
    53
    Posts
    33
    Rep Power
    0

    Re: A strange problem

    could this be it??

    In the winter the temperature drops below zero and the pressure drops with it.When the comp starts it's dischards pressure cannot rise fast enough to get a desent suction pressure.

    Just a guess

    Kind regards Art

  6. #6
    Join Date
    Aug 2007
    Location
    Southern New Jersey
    Posts
    11
    Rep Power
    0

    Re: A strange problem- ?

    Assuming all to be well with the system; proper charge and so forth, I would install a time delay low pressure control.

    It may well be that the system has an LP with a time delay but the time delay function of the control has failed.

    Or possibly the time delay low pressure control was replaced with a standard LP control by the unknowing.

    PHM
    ---------

  7. #7
    Join Date
    Apr 2008
    Location
    Ladysmith
    Posts
    8
    Rep Power
    0

    Re: A strange problem

    30secs, not enough time for pressure to balance in the system Maybe L.p switch cut out too high. Put some gauges on, override l.p switch & wait & see what happens on your gauges. if your pressure is correct it could be that your l.p switch is faulty or the electronics on the board which give the errors. also you could try & move the condensor to a warmer location like an enclosed area if your temps are too low but make provisions for heat in summer.

  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: A strange problem

    How cold is it when you get this problem?
    You say it's old, but then mention an inverter. Is it 8 years old, or way older?
    Is it just a regular type split, or a custom unit? make/model?
    30 sec is way too quick to fall over.
    It's definitely a tough call to make, could be a faulty r/v valve, or pressure control, or it may need modifications depending on ambient, type and design of unit.
    If you can't get make/model, ambients, refrigerant pressures and temps, r/v operation verified etc then you need an a/c tech to check

  9. #9
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    16

    Re: A strange problem

    Someone has to put gauges on it to see if the press is really low enough to give a lp trip.this may be stating the obvious but you are still using this unit in cooling mode what is your ambient temp type of throttling control and unit model before you provide full information any answers can only be speculation.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: A strange problem

    Could be that as the OP was in February last year and he hasn't replied that the problem is resolved, or he's given up
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: A strange problem

    Quote Originally Posted by chillin out View Post
    Could be a sticky 4 way valve.

    Needs a tech to put some guages on it though.

    Chillin
    Can a sticky 4wv cause a low pressure fault?

    Multisync
    London

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: A strange problem

    Quote Originally Posted by Brian_UK View Post
    Could be that as the OP was in February last year and he hasn't replied that the problem is resolved, or he's given up
    Could be, but we are stubborn as mules and have ego as mountains, and need to express our solutions no matter how late it is!

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: A strange problem

    Quote Originally Posted by nike123 View Post
    Could be, but we are stubborn as mules and have ego as mountains, and need to express our solutions no matter how late it is!
    I just wish sometimes, just sometimes, that we would get some feedback from the first poster

    It doesn't cost much to be polite
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  14. #14
    Join Date
    Jul 2007
    Location
    LIbya
    Age
    58
    Posts
    72
    Rep Power
    17

    Re: A strange problem

    I agree with viking,and the system should has the correct refrigerant quantity.
    best regard

  15. #15
    Csquared's Avatar
    Csquared Guest

    Re: A strange problem

    Not on an AC.