    I live in New York, when ever the outside temperature is lower then the freezing point, my walkin cooler stops cooling. The condenser of walkin cooler is on the roof of the building, size of walkin cooler is 6 ft X 20 ft. I hope some one can help me on this topic
    Thank You
    Arif



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Walkin cooler

    Hi Masooda and welcome to the forum.

    It sounds as though that due to the low outside temperature the refrigerant pressure within your cooling system is unable to rise above a low limit switch and start the unit.

    This could be due to a out of adjustment pressure switch or perhaps a slight shortage of refrigerant but it seems that the systems needs looking at by a refrigeration technician.
    Last edited by Brian_UK; 08-02-2007 at 07:53 PM. Reason: Forgot to say hello.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    masooda's Avatar
    masooda Guest

    Re: Walkin cooler

    Thank You

  4. #4
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: Walkin cooler

    Hi Masooda;
    Brian is of course correct.
    A trick often used (although I am not recommending it) is to put a heat source such as a light bulb up near the Compressor. Of course this can cause a fire. If you have a Refrigeration Mechanic come out and install some sort of crankcase heater on the compressor your problem will go away.
    I love simple service calls like this.

  5. #5
    Join Date
    Feb 2007
    Location
    England
    Age
    68
    Posts
    9
    Rep Power
    0

    Re: Walkin cooler

    This problem use to happen all the time when I was a lad because system temperatures were controlled by LP's. In summer we would have to adjust LP's to a higher range to stop them freezing the product and then in winter we have to go round again to lower them as the units would not cut in at all, happened mostly on hermetics, things ligh 3/4" Visions and other high temperature cases. Good business though, got paid for each call out.