    ASPERA compressor



    Hi My name is James and I do hand engraving. The tool I use is powered by an ASPERA compressor. The model # is T2134A it will not fully compress to 120LBS and it will not shut off. Any help . Thanks James



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: ASPERA compressor

    Quote Originally Posted by 541jamesw View Post
    Hi My name is James and I do hand engraving. The tool I use is powered by an ASPERA compressor. The model # is T2134A it will not fully compress to 120LBS and it will not shut off. Any help . Thanks James
    Hi jamesw

    I'm affraid it has bit the dust and stopped pumping get rid of it.

    Regards
    Lrac

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: ASPERA compressor

    Quote Originally Posted by 541jamesw View Post
    Hi My name is James and I do hand engraving. The tool I use is powered by an ASPERA compressor. The model # is T2134A it will not fully compress to 120LBS and it will not shut off. Any help . Thanks James
    Fridge compressors are sometimes used for air compressors.
    If it does not pump the same now then unfortunatley it would appear to be faulty.
    Any hermetic compwill replace it.

    Cheers taz.

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: ASPERA compressor

    I take it you have checked for air leaks?

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: ASPERA compressor

    Hi James,
    I've come across refrigeration style hermetic compressors used for air compressor applications before.
    One problem with compressing air is MOISTURE.
    In the particular case that springs to mind, the user had not been instructed in the need to drain the air receiver (tank) on a regular basis, or to run the unit when draining for a sufficiently long period such that the moisture is driven from the compressor.

    Often with these small units with low air consumption, the compressor only runs for short periods. Consequently, it does not have enough running time for it to get hot enough and condensation forms inside the compressor internals.
    This causes rusting of the internals and failure results.
    As with refrigeration use, these compressors are designed to only pump gas, not liquid ...any liquid such as condensation or worse still, water backup from the receiver (air Tank) due to not having been drained will kill the compressor.
    Advice is to drain the tank daily or weekly depending on level of use. I would then let the compressor pump for a good 10-15mins allowing it to discharge to air allowing to really warm up and drive any moisture out.
    Does this unit have an oil level sight glass / drain point? If so do you ever change the oil?
    You will need to replace your compressor but then learn to look after your new one.