    BCN, Spain
    43
    Velocities of R404a
    Hi everybody
    I`m trying to dimensioning some refrigerant pipes, but I don`t know wich are the recommended refrigerant velocities. Could someone recommend me some values for the different system lines (suction, liquid, discharge, hot-gas defrost)?
    I`m using Solkane solution for this calcs, but If anyone have a different solution, I`m all ears.
    Thanks a lot.
    RCR
    Apr 2005
    Canada
    69
    23
    Re: Velocities of R404a
    Danfoss has software. They call it "DIRcalc".
    I am in Canada and I find that the Solkane software has funny copper pipe sizes. Danfoss is better in that regard.
    The Dupont web site has some information. I had downloaded it but I cannot find the link. They give velocity and pipe size charts. Not as convienient as software but a good guide.
    Finally I am told that if POE oil is used it is completely miscible with R404a and velocity is not an issue. I am also told that there are minimum velocities that must be considered in suction and discharge llines. The numbers that I have found are 4-15m/s and 8-12m/s for vertical risers and 0.3-1m/s for liquid lines. And as always pressure drop must be a consideration.
    If you find anything else I would be interested in hearing from you.
    Oct 2005
    nottingham UK
    109
    http://us.refrignet.danfoss.com/SW/U...n_us/index.htm
    i think this is the link to the danfoss site to download the information
    regards
    Apr 2005
    Canada
    69
    23
    Yes that's the link.
    Thank you
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, all
    This is old version 1.13...
    Quote Originally Posted by davej View Post
    regards
    try this one: Ver 1.14
    http://www.danfoss.com/NR/rdonlyres/...DirCalc114.zip
    Best regards, Josip