Cable tray for refrigerant Piping
Can anyone tell me about the fixing standard for
tray in the riser and in roof for refrigerant piping for
ducted split Unit
Senthil
-
07-02-2007, 07:23 PM #2
Re: Cable tray for refrigerant Piping
Fixing distances are the same regardless of what the pipework is being fixed to.
Pipework should be insulated and any brackets/clips etc should also be insulated.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
08-02-2007, 06:26 PM #3
Re: Cable tray for refrigerant Piping
not sure about your country but genral standard in uk is 1.5 metres between fixings
-
08-02-2007, 06:43 PM #4
Re: Cable tray for refrigerant Piping
Harsen
you can free down load some info for cable trays from http://chalfantcabletray.com/uploads...s_NEMA_Ve2.pdf
malik55
-
09-02-2007, 05:02 PM #5
Re: Cable tray for refrigerant Piping
Don't tie wrap the pipe to the tray in the riser, as the pipe could slip inside the insulation and cause a probelm with the vapour seal. If you pull the tie to tight it will cause a failure of the insulations integrity.
Best to clip with Insualted HYDRO-ZORBS or CUSH-CLAMPS on channel.Last edited by michael7; 13-02-2007 at 05:07 PM.
-
13-02-2007, 02:02 PM #6
Re: Cable tray for refrigerant Piping
Thank you malik for the link , its very useful to me
Senthil