    Acidic oil



    In reading between the lines of some of the threads I can almost anticipate some of the answers.
    But has anyone tried the additive Acid away by rectorseal.
    It's an additive to chemically neutralise acids after burnouts,or such.
    t seems to have wraps, well it would. for some satisfied customers I believe trane recommend it's use it according to the hype from the supplier. Just wondering what you guys think



  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    The Prof might be a bit biased on this subject, but he believes he reiterates what most of the folks on this forum consider appropriate service practice regarding this subject. This can be summarized as follows:

    1. Avoid adding anything to the refrigerant or oil.... The chemistry resulting from using these additives can have unintended consequences.

    2. To maintain a dry and acid free system, you are far better off using a filter-drier having suitable acid and water capacity.
    Prof Sporlan

  3. #3
    Join Date
    Jul 2001
    Location
    West Lothian, UK
    Posts
    20
    Rep Power
    0
    I believe it works by reverting the acid back to moisture, it does not actually remove any moisture, so if you do not follow good refrigeration practice and use the approporiate clean up driers it will return after a period of time.

    A more cynical person could say that it is a gimmick to fool acid test kits.

    David Allan

  4. #4
    Join Date
    Apr 2002
    Location
    Pennsylvania, USA
    Age
    55
    Posts
    78
    Rep Power
    0
    Originally posted by dwallan

    A more cynical person could say that it is a gimmick to fool acid test kits.


    And that person would be me.

    AI feel that acidaway is as much snake oil as thawzone. Good drier practice and oil changes eliminate problems masked by these chemicals.

  5. #5
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    I have used acid away and another similar product out of desperation on really fouled up large systems. Heck, I have used thawzone (meaning I have techs that use it) a number of times.

    If something good could be said about acid away it is that the Ph of the fluids is reset to what we hope is closer to neutral. It buys time and hopefully prevents damage in the short term. In extreme circumstances, I use it. But then oil changes, filter changes with hh driers, for as long as a month.

    I now wonder if molecular seive driers would trap the detritus of neutralized acids more effectively than combo alumina gel/molecular seive driers. Hmmm.

  6. #6
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    I now wonder if molecular seive driers would trap the detritus of neutralized acids more effectively than combo alumina gel/molecular seive driers. Hmmm.
    Dan, of course, you simply mean "alumina/molecular sieve" filter-driers. Silica gel isn't used any longer as a desiccant in refrigeration filter-driers, at least U.S. manufacturers no longer use it....

    The "detritus" of neutralized acids is invariably water. Yes, moelcular sieve has a high water capacity, and would be effective when used with an acid neutralizer. Unfortunaltely, molecular sieve has a low acid capacity. Far better to use an alumina/molecular sieve filter-drier, and take care of both problems...
    Prof Sporlan

  7. #7
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    The "detritus" of neutralized acids is invariably water.
    I thought there might be some salts, as well.

  8. #8
    Join Date
    Dec 2001
    Location
    Cincinnati, Ohio, USA
    Age
    63
    Posts
    258
    Rep Power
    23
    It makes you wonder if you might as well open an accumulator and toss in a rock......

  9. #9
    Join Date
    Apr 2002
    Location
    Pennsylvania, USA
    Age
    55
    Posts
    78
    Rep Power
    0
    Maybe a hunk of coral...

  10. #10
    Join Date
    Apr 2001
    Location
    Tyler, Texas
    Age
    53
    Posts
    12
    Rep Power
    0
    I have used acid away when we have a real bad burn out. But I also replace drier plus install suction filter drier, new refrigerant. Then After 24 to 48 hours( depends on how large of system) we retest the oil,. If system test bad We change the oil, add acid away, and new filters again. WE also use acid driers for burnout to clean the system up..
    Preston Roy Powell
    www.thinkcool.net

  11. #11
    Join Date
    Dec 2001
    Location
    Canada
    Age
    70
    Posts
    52
    Rep Power
    23
    Continous acid tests - Oil and drier changes until the system tests clear... Hold the additives!

  12. #12
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28
    As far as I am aware, Trane do not allow the use of any additives whatsoever in any of their equipment.

  13. #13
    Join Date
    Aug 2006
    Location
    United States
    Posts
    7
    Rep Power
    0

    Re: Acidic oil

    My company manufactures an acid treatment that uses the filter drier and not a dangerous chemical reaction to treat acid. This forum was making me laugh because in our marketing meetings some of the head honchos keep repeating that "we need to educate the consumer that the competing products cause dangerous chemical reactions blah blah blah etc. etc." So I see this forum and it looks like everyone realizes exactly what is going on lol. Anyways take a look at it here, http://www.qwik.com/products/qwikshot.html this treatment does not neutralize the acid or cause a chemical reaction. It just moves it all to the filter-drier really quickly, the only set-back is that it has to be hermetically injected rather then just dumped in like "acid-away".

  14. #14
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Acidic oil

    in other words it is a simple preferential Carrier to the acid, with a molecular affinity to standard absorption F/Ds ?

  15. #15
    Join Date
    Aug 2006
    Location
    United States
    Posts
    7
    Rep Power
    0

    Re: Acidic oil

    I am going to walk over to the chem lab and ask our chemist John Meyer, but I think you hit the nail on the head.

  16. #16
    Join Date
    Aug 2006
    Location
    United States
    Posts
    7
    Rep Power
    0

    Re: Acidic oil

    John has given your statement his stamp of approval

  17. #17
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Acidic oil

    Ah K then I'd give it my stamp of trust to try it out some day.