    furnace troubles



    I have a 75,000 btu input Arco Air gas furnace that was converted to LP gas when it was installed in 2000 that wasn't working properly. I went out on the call and only one of the burners would light. I noticed that the three burners were all carboned up. I cleaned the burners and the thing lit all three of them. As it ran the flames would occassionally creep back into the burner assembly. But it wasn't really a lazy flame like a venting problem. It would just creep back into the mixing chamber periodically. I checked the gas pressures inlet and outlet of the gas valve both were good. ( 12 in wc inlet and 10 in wc outlet). I disconnected the vent pipe but it did not mater. I am suspecting maybe a small crack in the heat exchanger just enough to effect the draw of combustion gas into the heat exchanger but I am not sure. I was hoping that you guys might offer some insight.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: furnace troubles

    I don't think that you will see replies to a post of burners in a refrigeration forum.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Jan 2007
    Location
    SPAIN
    Posts
    172
    Rep Power
    18

    Re: furnace troubles

    Check out h__p://___.hvac-talk.com/vbb/
    on your side of the water... plenty to read there.

  4. #4
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    58
    Posts
    723
    Rep Power
    22

    Re: furnace troubles

    I can't comment on the equipment that you are working on as we don't have this make of kit, but if any of the burners are carboned up, the you have a serious ventilation problem that needs to be sorted out, the air supply is not enough for the furnace input
    Karl

  5. #5
    Join Date
    Apr 2006
    Location
    US
    Posts
    10
    Rep Power
    0

    Re: furnace troubles

    Thanks for the info Karl. I talked with the manufacturer and they thought that I should replace the gas valve. They stated that moisture could settle in the valve and small particles of water would enter the mixing chamber and cause a sputter and allow the flame to enter the chambers causing the black soot. But I think you are correct about the combustion air lacking causing the black soot because air would be lacking in the chambers. Thanks again for the help.

  6. #6
    Join Date
    Apr 2006
    Location
    US
    Posts
    10
    Rep Power
    0

    Re: furnace troubles

    Quote Originally Posted by momo View Post
    Check out h__p://___.hvac-talk.com/vbb/
    on your side of the water... plenty to read there.
    Thanks for the info. I will check it out.