    Friction los calculation lines



    We use for the calculation of the friction loss along the lines the formula

    Dp = Re x L x rho x V(square) /d/2 where rho is the density of the refrigerant in that line, d= inner diameter, L = length of the line (and additional the equivalent length of the bends in this line) and Re the Reynolds number of the used copper.

    Literarture I have gives me Re numbers from 0.015 to 0.035 (or a differencee of +/- 250% which can give me a friction loss difference of 250%)
    Does anyone have more accurate numbers because you then better guess the friction loss?

    Or does someone use another formula to calculate this?
    Last edited by Peter_1; 31-01-2007 at 10:32 PM.


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Friction los calculation lines

    Hi, Peter_1

    Is this of some help

    Best regards, Josip
    Attached Images Attached Images

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Friction loss calculation lines

    Thanks Josip but I think I have the same problem: what do I have to take for 'f' ??

    Formula 3 inlet and outlet pressure, that's now exactly what I need to calculate.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Friction los calculation lines

    Peter,

    Here is a link to some material that may help you.

    http://arash.dejkam.com/software/pressure_loss/

    I think it is in IP, but it shows the process of calculation.

    The "f" is the friction factor which you need to find the pressure loss. The friction factor is read from the Moody diagram once you find the Reynolds number.

    I'm still looking for an SI version, so you do not have to do unit conversions.

    Have patience...

    Edit:

    Perhaps this will help you Peter.
    http://www.engineeringtoolbox.com/da...ion-d_646.html
    Last edited by US Iceman; 01-02-2007 at 01:24 AM. Reason: added info for my Belgium friend!

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Friction loss calculation lines

    Hi, Peter_1

    Quote Originally Posted by Peter_1 View Post
    Thanks Josip but I think I have the same problem: what do I have to take for 'f' ??

    Formula 3 inlet and outlet pressure, that's now exactly what I need to calculate.
    Take a look at this:

    http://www.engineeringtoolbox.com/da...ion-d_646.html
    http://www.engineeringtoolbox.com/co...on-d_1031.html

    and

    Quote Originally Posted by US Iceman
    Have patience...
    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •