Re: Frick Quantum LX Compressor control panel: Capacity Control Screen
Hi, Screw_geek
According to your values:
SP=20 psig
NZ= 0.5 psig 0.5 psig
PB= 15 psig 15 psig
Cycle time 3 sec 3 sec
Seems you can set you NZ as you like around SP and the same is for PB. Time to engage solenoids you can also change up maybe from 0.5 sec up to 3 sec both for up and down.
You must play with those values but you can try
SP=20
NZ= 0.5 psig 0.5 psig
PB= 5 psig 5 psig
time down 3 sec time up 2 sec
Once you set your NZ and PB it will come along with any SP you set.
Please take a look at attached file:
Best regards, Josip