    Screw discharge cooling



    Hi guys,

    Somebody told me about cooling the booster screw discharge with liquid injection directly into the discharge pipe eliminating the intercooler, thus the booster discharge would be the high stage suction and we can save money eliminating the intercooler besides the pressure discharge to be smaller than those with intercooler.

    Does anybody has any experience about this?

    Best regards,

    Volnei



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, Volnei, this is a common design on two stage NH3 systems at present. I first seen this concept on Grasso screws, with the low stage compressor discharging directly into the high stage suction, both compressors are fitted on the same base plate. There is another connection at the interstage this is a suction or economiser feed, usually from an open flash economiser, this is what makes the cycle efficient with the subcooling of the liquid using the intermediate pressure.
    Regards. Andy.
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Apr 2007
    Location
    Phillipine
    Posts
    22
    Rep Power
    0

    Re: Screw discharge cooling

    Hi,
    If these is one is one booster to high stage can be I also seen these system use on the CO2 recovery system from a brewery but for multiple booster compressor and multiple high stage compressor it is not applicable the volume of gas is big and can't be taken by just one high stage compressor

  4. #4
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Screw discharge cooling

    I have seen it used on a freeze drier to good effect and the pipe between the single machines was around 3 feet long.

  5. #5
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Screw discharge cooling

    On this type system, the high stage compressor generally does not have any injection oil fed to it. It gets enough oil from the booster. If they are short coupled and no side load at the intercooler level, they are generally started at the same time.

    Ken

  6. #6
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Screw discharge cooling

    correct, we had a solenoid on the oil feed to high stage to shut it off when the booster starts. but we now try to reccomend the danfoss akv to cool delivery on liquid injection. using the EKC 319A.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Screw discharge cooling

    all good in theory, but similar to a hand grenade with a loose pin. Good luck. Magoo

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Screw discharge cooling

    Hi, Magoo

    Quote Originally Posted by Magoo View Post
    all good in theory, but similar to a hand grenade with a loose pin. Good luck. Magoo
    agree with you...but original post is from 2002....

    I made a similar one cold store installation in the year 1984 (4 screws buster (-35*C/-45*C) + 4 screws high stage (-10*C/35*C).....good Sabroe design..., but with a lot of small adjustments to start up the plant.....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Screw discharge cooling

    Quote Originally Posted by Josip View Post
    Hi, Magoo



    agree with you...but original post is from 2002....

    I made a similar one cold store installation in the year 1984 (4 screws buster (-35*C/-45*C) + 4 screws high stage (-10*C/35*C).....good Sabroe design..., but with a lot of small adjustments to start up the plant.....

    Best regards, Josip
    yeah ... talking about date/time ...
    some of our fellow "speakers" do not have their time/date displayed 'correctly' ... i wonder why?

    i've seen such installation in compound compressors [2-stage compressor] but then some still insist shell & tube intercooler prior to connection to high side suction.

    in my opinion, intermediate HE still preferable to eliminate nuisance in ctrls.

  10. #10
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Screw discharge cooling

    Hi, Hendry

    Quote Originally Posted by hendry View Post
    yeah ... talking about date/time ...
    some of our fellow "speakers" do not have their time/date displayed 'correctly'
    ... i wonder why?
    ???

    Quote Originally Posted by hendry
    i've seen such installation in compound compressors [2-stage compressor] but then some still insist shell & tube intercooler prior to connection to high side suction.

    in my opinion, intermediate HE still preferable to eliminate nuisance in ctrls.
    agree with you....


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  11. #11
    Join Date
    Feb 2008
    Location
    Napa, CA
    Age
    54
    Posts
    33
    Rep Power
    0

    Re: Screw discharge cooling

    Directly injecting liquid into the discharge Vs. an intercooler in a two stage system. The question was about energy savings. I will comment on one thing. A BTU is a BTU. If it takes the same amount of refrigerant to cool the discharge gas from the low side machine to the high side machine the only penality of a systems intercooler would be pressure drop. Does this make sense? There have been practicianers of both designs for 30+ years.

    Hussmann refrigeration used to make the TD System (designed by Cap Blake) 40 years ago that used liquid injection with R-502. I was a neat peice of two stage design.

    Ammonia system designers used intercoolers so they could control the exchange with more safety.

    I believe that a single stage is more efficient with less parasitic losses if the comression ratio allows...

  12. #12
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Screw discharge cooling

    Quote Originally Posted by Core4 Guy View Post
    Directly injecting liquid into the discharge Vs. an intercooler in a two stage system. The question was about energy savings. I will comment on one thing. A BTU is a BTU. If it takes the same amount of refrigerant to cool the discharge gas from the low side machine to the high side machine the only penality of a systems intercooler would be pressure drop. Does this make sense? There have been practicianers of both designs for 30+ years.

    Hussmann refrigeration used to make the TD System (designed by Cap Blake) 40 years ago that used liquid injection with R-502. I was a neat peice of two stage design.

    Ammonia system designers used intercoolers so they could control the exchange with more safety.

    I believe that a single stage is more efficient with less parasitic losses if the comression ratio allows...
    hola!
    sometimes it is a bit hard to draw a line between which is correct/better than the other. i feel it depends on whom you kick start your experiences with.
    anyway, the most important is still the design must works.
    Hendry

    "What uncertainty means to you, and you only?"

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Screw discharge cooling

    Well done all the picky picky ones, I joined 07 and did note the original posting date. Now you are all full of comment.
    Well there ya go.
    magooooo

  14. #14
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Screw discharge cooling

    as soon as you take the compressor compression ratio up you are doing more work - higher kW used simple. There is a limit where single stage just stops being a good decision but i have commissioned too many plant with a COP less than one due to the fact "the compressor can do it." Two compressors doing the duty is often more efficient than a single stage just look at COP achievable with two stage two tmp cooling plants i have on working at a COP of 7. Its much better for loads to two stage plants but customers are shortsighted with plant install costs and then question the electric bill at the end of the month. Two stages is a good simple idea which works very efficiently with oil cooling instead of liquid injection for compressor cooling. It is one of my biggest problems when customers "prefer" single stage because they don't understand a little extra money now will save a fortune over time.

    Sorry rant over.

Similar Threads

  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  2. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  3. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM
  4. Exploded discharge line
    By Peter_1 in forum Industrial
    Replies: 1
    Last Post: 05-05-2004, 09:47 PM
  5. Regulation of cooling capacity
    By npaisnel in forum Domestic
    Replies: 13
    Last Post: 08-02-2002, 11:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •