    Ice Bank Tank for Chilled Water



    Could some one tell me wether an Ice Bank Tank could be replaced with a Shell & Tube Chiller or a Plate Heat Exchanger. The temperature of water is required at 4 Deg. C with water coming at 30 Deg. C. The required flow is 35 lpm. This is required for a process chilling. The requirement is for an Ice Bank Tank, and I am thinking that instead of Ice Bank Tank, why don't I install a compact chilling plant.

    Advice and suggestions shall be highly appreciated.



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Ice Bank Tank for Chilled Water

    Hi Samarjit Sen

    can't think of any reasons why you can't use a plate heat exchanger, but other members mgiht have a diffferent view.

    Regards
    Lrac

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ice Bank Tank for Chilled Water

    One of the biggest advantages of using ice for thermal storage is the the large volume of stored capacity that is available.

    Sure, a small chiller package will work but it will probably be a larger cooling capacity, rather than that of the refrigeration system for the ice bank.

    It depends on several variables:

    How much cooling is required instantaneously with the ice bank?

    How much time is available to build the ice, and how much time is required for the actual process cooling load.

    If there are large time periods between the process cooling cycle requirements, then an ice bank is preferable in my mind. This would also offer the smallest refrigeration system as you are storing the cooling (in ice) over a long time duration.

    If the process cooling is almost continuous, then a chiller water system with a chiller would probably be a better choice. In this case, the refrigeration system could be much larger (than the ice bank system), since you are meeting the cooling demand as it occurs.
    Last edited by US Iceman; 28-01-2007 at 03:48 AM. Reason: spelling

  4. #4
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Ice Bank Tank for Chilled Water

    I understood one reason for using an ice bank was that you could produce ice overnight on cheap rate power and then use the ice to meet or supplement demand during the day. (Load lopping).
    In this way you can run a smaller chiller during the day and another small one at night with a lower set point to freeze the ice. More efficient.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ice Bank Tank for Chilled Water

    Quote Originally Posted by Electrocoolman
    I understood one reason for using an ice bank was that you could produce ice overnight on cheap rate power and then use the ice to meet or supplement demand during the day.
    That's true also. Areas of high demand charges are one those things that make ice storage very economical.

    However, not all ice banks use chillers. This is something of a relatively new idea. Until this started almost all of the ice bank storage systems used flooded or recirculated liquid feed (mostly ammonia).

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Ice Bank Tank for Chilled Water

    In our country the rate of electricity is the same round the clock. I am trying to think in terms of having a compact plant with more efficiency. A plant of 35 lpm is small and the refrigeration load in this particular case will not be much. I had assessed the load at 56 kw at -5 Deg. C Te and 35 Deg. C Tc with R 22 as a refrigerant.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Ice Bank Tank for Chilled Water

    Probably the ice tank was installed or required because of the high delta T in/out. S&T and PHE require a minimum flow to ensure turbulence, and as known flow is inversely proportional to delta T. There may not be exchangers for that capacity and that delta T on the market, which would require a custom made exchanger.
    Last edited by NoNickName; 28-01-2007 at 04:54 PM. Reason: spell checl

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ice Bank Tank for Chilled Water

    Hi, Samarjit Sen

    Quote Originally Posted by Samarjit Sen View Post
    Could some one tell me wether an Ice Bank Tank could be replaced with a Shell & Tube Chiller or a Plate Heat Exchanger. The temperature of water is required at 4 Deg. C with water coming at 30 Deg. C. The required flow is 35 lpm. This is required for a process chilling. The requirement is for an Ice Bank Tank, and I am thinking that instead of Ice Bank Tank, why don't I install a compact chilling plant.

    Advice and suggestions shall be highly appreciated.
    Quote Originally Posted by US Iceman
    Sure, a small chiller package will work but it will probably be a larger cooling capacity, rather than that of the refrigeration system for the ice bank.
    Quote Originally Posted by Electrocoolman
    In this way you can run a smaller chiller during the day and another small one at night with a lower set point to freeze the ice. More efficient.
    Agree with guys...

    It is not so small capacity and speaking about optimization I will suggest to stay with Ice bank.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Ice Bank Tank for Chilled Water

    Quote Originally Posted by US Iceman View Post
    However, not all ice banks use chillers. This is something of a relatively new idea. Until this started almost all of the ice bank storage systems used flooded or recirculated liquid feed (mostly ammonia).
    We've one (Packo) and it's a DX one on R404a.
    But another good example is the Cristopia Energy Systems from France (VEnce) with the frozen balls in the storage containers
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ice Bank Tank for Chilled Water

    Quote Originally Posted by Samarjit Sen
    I had assessed the load at 56 kw at -5 Deg. C Te and 35 Deg. C Tc with R 22 as a refrigerant.
    But what was the capacity of the refrigeration system on the ice bank? My guess is the capacity was considerably smaller.

    Although, the packaged chiller would offer a smaller installation in all probability.

  11. #11
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: Ice Bank Tank for Chilled Water

    The ice tank allows you to use a smaller chiller and it also is used as a buffer tank most likely. I have seen chillers installed in low temp applications and the chiller is constantly cycling due to load changes. I have installed buffer tanks to stop the short cycling, I would leave the tank.

    Is the chiller pumping in and out of the tank on its own loop? Is the load from the tank on a seperate loop?

  12. #12
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Ice Bank Tank for Chilled Water

    The application for which I am thinking to provide a chilling plant than an Ice Bank Tank, is that the chilled water from the chiller shall cool milk after pasteurising in batches. The chilled water flow is 35 lpm and the refrigeration capacity of the system is 56 kw. I propose to maintain the Te at -8 Deg. C and the Tc at 35 Deg. C.

  13. #13
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ice Bank Tank for Chilled Water

    Hi, Samarjit Sen

    Quote Originally Posted by Samarjit Sen View Post
    The application for which I am thinking to provide a chilling plant than an Ice Bank Tank, is that the chilled water from the chiller shall cool milk after pasteurising in batches. The chilled water flow is 35 lpm and the refrigeration capacity of the system is 56 kw. I propose to maintain the Te at -8 Deg. C and the Tc at 35 Deg. C.
    That capacity is per/h but I think you have much more milk to cool but only in the morning i.e. once per day if I am right..

    Quote Originally Posted by Us Iceman
    If there are large time periods between the process cooling cycle requirements, then an ice bank is preferable in my mind. This would also offer the smallest refrigeration system as you are storing the cooling (in ice) over a long time duration.
    Attached is a photo of special ice bank silos in one dairy. The same compressor is running on day time for AC purpose and over night to make ice (good optimization ).

    Best regards, Josip
    Attached Images Attached Images

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  14. #14
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Ice Bank Tank for Chilled Water

    Hi Samarjit Sen

    All of the ones ive seen have used ice bank systems, but these were small scale dairies based on the farm (200L-10,000L a day).
    How continuous is the flow of milk through the pasturiser? If they stopped the flow to change the temperature recorder paper for example and the chiller goes off and they start the milk flow again while the chiller is waiting to start (6-10 minutes between starts?) would this cause problems?
    Maybe you would need a buffer tank to hold enough chilled water to run the pasturiser if the chiller is cycling off and on.
    I'd vote for an ice builder, but thats because they are what im used to

    Cheers Jon

  15. #15
    kevinlewis1970's Avatar
    kevinlewis1970 Guest

    Re: Ice Bank Tank for Chilled Water

    I worked for a company who removed a a large ugly ice bank. W e replaced it with a WITT SPRAY CHILLER. It is basically a shell and tube heat exchanger with a liquid pump at the bottom. The pump pumps liquid ammonia to a a pipe internally above the tube bundell and sprays a fine mist of ammonia over the tube which can give you temps as low as 0.7'C with water at a required flow rate.
    W e used a Mycom screw and a small evaprative condensor. The plant was very compact and extremly efficent with a 120kg ammonia charge.

  16. #16
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Ice Bank Tank for Chilled Water

    The milk shall be chilled throughout the day. The total capacity of the milk which has been estimated by the user shall be 7 to 10000 liters per day. The operation shall continue for the working period which may be only 12 hours at the most in the day time. There shall be no operation in the night.

    The process shall be continuous as there are are no temperature recorder and there is no need to change any paper.

    I do not think that the quantity of milk shall be more than 5000 liters per day. I have considered the maximum. Further the milk shall be cooled in batches, which means that there shall time when the chiller shall be running on no load.

  17. #17
    bakianathan's Avatar
    bakianathan Guest

    Re: Ice Bank Tank for Chilled Water

    where can i learn the basics of IBT system.

  18. #18
    pra1968's Avatar
    pra1968 Guest

    Re: Ice Bank Tank for Chilled Water

    Quote Originally Posted by kevinlewis1970 View Post
    I worked for a company who removed a a large ugly ice bank. W e replaced it with a WITT SPRAY CHILLER. It is basically a shell and tube heat exchanger with a liquid pump at the bottom. The pump pumps liquid ammonia to a a pipe internally above the tube bundell and sprays a fine mist of ammonia over the tube which can give you temps as low as 0.7'C with water at a required flow rate.
    W e used a Mycom screw and a small evaprative condensor. The plant was very compact and extremly efficent with a 120kg ammonia charge.
    Dear Kevinlewis1970
    can u explain more abt it?
    I m also intrested in it to use for chilled water !!!

  19. #19
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Ice Bank Tank for Chilled Water

    I don't know about India, but in the Netherlands they do not allow the use of glycol without a dubble separation from the foodstuff. Glycol will have to be used in this case. If one uses an ice buffer, this can also be used as a separation by running the proces water through the ice banks.

    But I could be way off track here!
    If it ain't broke, don't fix it!

  20. #20
    gueito's Avatar
    gueito Guest

    Re: Ice Bank Tank for Chilled Water

    Hi! I'm designing a refrigeration system for a dairy industry. I was thinking of using an ice bank but I don't know which cycle to use. Do I need to use a booster or only one compressor? Can anybody provide me with a drawing of the cycle? I need a load of 55 TR.
    Thank you

  21. #21
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Ice Bank Tank for Chilled Water

    What ever all the above. The only advantage of ice banks is peak loading in short time frames. So you build ice in the ice bank, more than likely at off peak power loadings, and then consume the ice during production.
    Load profiles are the real criteria.
    magoo

  22. #22
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: Ice Bank Tank for Chilled Water

    What i know is that ice banks are usually installed to get advantagues of low electricity cost during night. Another reason which make ice bank worth installing that, if the peak hours of a building required big plant to overcome heat load in a very limited time during the day . An example for that is a factory crowded messhall where the need of cooling is only in the time where workers are enjoying their hot meals. In that case ice bank offers capital cost saving and low power consumption as the build up of ice is usually made during night when the electricity cost is lower. It's also worth installing in milk producing farms.
    Last edited by Shibhrac; 16-09-2009 at 10:23 AM.

  23. #23
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Ice Bank Tank for Chilled Water

    Another option is binary ice, (slush)
    Higher averaged COP than a standard ice builder, reduced heat transfer area, piping and pumps required,

  24. #24
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Ice Bank Tank for Chilled Water

    Hi
    low electricity cost during night +
    ice banks is a suitable for peak loading in short time
    Also in ice bank your temperature can comes to near 0 without damaging Evap. but in chiller you cannot go temperature of water less than +5 . Your evap. temperature does not allow you and it is very dangerous

  25. #25
    Join Date
    Nov 2008
    Location
    India
    Age
    83
    Posts
    17
    Rep Power
    0

    Re: Ice Bank Tank for Chilled Water

    Ice Bank System is selected where load is 4-6 Hrs/day.Refrigeration syatem is selected of capacity 20-25% & it runs for 20-24 hrs/day. Refrigeration is stored in form of ICE,which melts on load.

  26. #26
    Join Date
    Nov 2008
    Location
    India
    Age
    83
    Posts
    17
    Rep Power
    0

    Re: Ice Bank Tank for Chilled Water

    Quote Originally Posted by gueito View Post
    Hi! I'm designing a refrigeration system for a dairy industry. I was thinking of using an ice bank but I don't know which cycle to use. Do I need to use a booster or only one compressor? Can anybody provide me with a drawing of the cycle? I need a load of 55 TR.
    Thank you
    What is quantity of Milk @ what is time in which U want to cool

  27. #27
    Join Date
    Nov 2008
    Location
    India
    Age
    83
    Posts
    17
    Rep Power
    0

    Re: Ice Bank Tank for Chilled Water

    Quote Originally Posted by Bhagwan Harani View Post
    What is quantity of Milk @ what is time in which U want to cool
    what quantity of milk U want to cool & time