    capacity issue



    hi everyone,got called to a site running a low temperature Thermogensis cabinet,set point at -42'C.
    anyway,the intial fault reported was oil failure,so upon arrival reset fault and monitor the compressor(a dorin 2s 2500)operation.as in the past the oil sight glass slowly refilled to half way and the darn thing kept on running.tested oil pressre,very good,checked oil sep,again ok.
    so i'm sitting there as usual scratching my head thinking this is a one off when the system cycles off at temperature,the control is a solonoid pumpdown type.after a few minutes or so the compressor cycles back on the lp diff,but only until it pumps down again,and again and again.
    because of this short cycling i suspect this is the cause of my oil migrating out of the comp. and not returning.
    further inspecting i find a sorit or PI type vavle fitted to the suction.this has been used to set up the evaporating pressure on the cabinet.
    this also has a pilot valve fitted with an hp signal.
    my question is(finally they say!),should this valve be able to provide capacity control to prevent the compressor pumping down and short cycling.
    it's been so long since i've seen a valve like this,i don't want to venture into the unknown and make the fault worse.
    the only visable info on the pilot is that it's a danfoss cvc type valve,and a vavle stem on the main body which is used to set evap.pressure.
    any helpful input would be greatly appreciated.

    cheers



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: capacity issue

    Hi 2cool4u

    The constant pump down operation will not help the situation and it may be the EPR valve gradually opening and allowing the pressure to rise and cause the comp to pumpdown again and again.

    I cant think why a suction valve would be required at those temperatures when it would have been better fitting a CPR.

    May be worth checking on that low temp if the oil sep has its own heater and the crankcase heater is ok.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: capacity issue

    Why not convert the constant pump down to a one-shot pump down?

    Lock out the pump down circuit until the next run period.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: capacity issue please help me

    Quote Originally Posted by epsilonoae View Post
    I need a evaporator coil for Carrier 40 Ton Condensing Unit Split System and tell u which is ur suggestion for Coil Construction Capabilities Tube sizes; Tube and Fin Materials; Headers and Protective Coatings for a Potato storage.
    ^ You win A$$ hole of the day award you know that? Spamming multiple forums is bad enough jacking some ones thread to spam one more time is just pathetic!

  5. #5
    Join Date
    Oct 2006
    Location
    london
    Age
    47
    Posts
    13
    Rep Power
    0

    Re: capacity issue

    thanks LRAC,just had a look at a danfoss website and indeed it looks like a PM1 CPR valve.i'll check the heater operation on sep and crankcase as well....
    roll on monday