    thermomax 100 probes



    hi
    keep having problems with evap probes.is this due to mouisture. anytime you take probe out and dry it fault clear.s.probe is in the back of the coil far left.half way down.electric defrost.is this the position it should be in.



  2. #2
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: thermomax 100 probes

    Hi John,

    It sounds like moisture. Have you tried replacing the probe for a new one?

    djbe

  3. #3
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: thermomax 100 probes

    Hi john howie

    i presume your using the metal tipped probes that come with the thermomax controller.

    Try getting the rubber sealed probes from HRP they are available for that controller.

    If you can't get them smear some silicon sealant around the bottom of the probe where the wires come out and that should solve your problem.

    regards
    Lrac

  4. #4
    Join Date
    Jan 2007
    Location
    glasgow
    Age
    53
    Posts
    13
    Rep Power
    0

    Re: thermomax 100 probes

    hi lads
    i have replaced it with the hrp rubber seal one,s but thought you could get other probes to suit controller

  5. #5
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: thermomax 100 probes

    you need a new probe to start with ,as for position,i allways put them in the side cover on the expansion valve side, on the top coil run tip facing upward so as not to let water make its way in, termination set at 8 deg,sometimes you need a bit more but by putting them there it stops the TEV icing up and coil ends,also is in the coldest part of the coil that needs to get its heat.i dont insulate them just strap in to the coil loop so it senses the serounding temp, works for me.

  6. #6
    Join Date
    Jan 2007
    Location
    glasgow
    Age
    53
    Posts
    13
    Rep Power
    0

    Re: thermomax 100 probes

    that side is totally iced up constantly due to coil being above a double door with curtain at a production area at plus 12 my room is set at 0c they will not change this set up

  7. #7
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: thermomax 100 probes

    sounds to me like thats the side you need to tackle, if the evaps iced up on the TEV side it will be part shut all the time and just getting worse,the probe where you have it is doing its job but in the wrong place, try my suggestions,you might just be supprised.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: thermomax 100 probes

    If it's a ntc or ptc probe, unwrap a condom, put the probe in it, pour some vinilic or siliconic glue, let it dry, strap, and cut the excess latex. You'll lose some readiness of response, but will gain precision and reliability.

  9. #9
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: thermomax 100 probes

    bit early for that kind of talk nick !!

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: thermomax 100 probes

    No pun intended.

  11. #11
    Join Date
    Jul 2004
    Location
    Scotland
    Posts
    51
    Rep Power
    20

    Re: thermomax 100 probes

    John,

    The defrost probe being halfway up the coil is wrong you should either have it at the top of the coil or on the coldest pass. If you put it on the coldest pass you should cover it with silver foil tape to help it read accurately.

    I would suggest that the TEV end is icing up first as it is the coldest point and you have a constant stream of warmer air coming from the production area.

    It is a bit of a compromise but I would suggest more frequent, shorter defrosts to prevent the ice from forming in the first place.

    David

  12. #12
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: thermomax 100 probes

    Quote Originally Posted by NoNickName View Post
    unwrap a condom, put the probe in it
    I carry a lot of kit in my truck but i couldn't explain that one away.

    Kind regards
    Lrac