    Exclamation artificial oils



    Dear friends:
    whats physical property of chemical result that has been caused of mixing artificial oils(polyesterin) with wet air?
    How can we be so sure about their safety during functional system?
    thanks in advance.
    s.pirs.


    S.P

  2. #2
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,086
    Rep Power
    25
    Polyolester oils are significantly more hygroscopic than mineral oils. Thus you will get more moisture into the system with a polyolester oil exposed to wet air than you would with a mineral oil exposed to the same amount.

    The most significant drawback is the formation of acids during the high temperature compression process, which will tend to cause further chemical reactions within the system such as copper plating, and insulation breakdown on the motor windings. If you suspect that the oil was exposed to wet air, you should take a sample and have an analysis done by a lab. The filter drier manufacturers have redesigned some of their filters to combat this likelihood.

  3. #3
    Join Date
    Mar 2002
    Location
    Tehran
    Age
    55
    Posts
    38
    Rep Power
    0
    Dear Sir Dan :
    Thanks for your attention and good technical advice .
    Is that true some type of them may get a bit plastic form after absorbing water ?
    and what temps are avoided at discharge line ?
    best regards
    S.P

  4. #4
    Join Date
    Mar 2001
    Location
    Derby, England
    Age
    57
    Posts
    86
    Rep Power
    24
    Sir Dan eh........you never told us......did you meet the corgis?

    Frosty

  5. #5
    Join Date
    Apr 2001
    Location
    Tyler, Texas
    Age
    53
    Posts
    12
    Rep Power
    0
    Well what happens is the oil turn to acid and the acid eat the winding of the compressor. If the system has a leak it needs to be found if some one repaired a leak and didnot change the drier or oil correctly it needs to be changed. THe new oil you have from 15 to 45 minutes to seal the system this also depends on the weater and humidity.
    Preston Roy Powell
    www.thinkcool.net

Similar Threads

  1. Oils
    By johnemar in forum Refrigerants
    Replies: 5
    Last Post: 26-05-2010, 08:37 PM
  2. refrigeration oils
    By dumpeyau in forum Fundamentals
    Replies: 4
    Last Post: 18-11-2009, 12:00 PM
  3. Refrigeration oils
    By johnemar in forum Refrigerants
    Replies: 2
    Last Post: 25-02-2003, 08:36 AM
  4. low PH oils
    By pirestani in forum Refrigerants
    Replies: 2
    Last Post: 24-10-2002, 08:05 PM
  5. R-22 with ester oils
    By Friobernal in forum Technical Discussions
    Replies: 7
    Last Post: 24-05-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •