    Pressure piping test



    I would like to know what is the procedure that you use to do pressure test piping after welding conclusion in a big plant with ammonia.

    Do you also do vacuum test?

    Best Regards.

    Volnei



  2. #2
    Join Date
    Aug 2001
    Location
    Halifax, Nova Scotia, Canada
    Posts
    6
    Rep Power
    0
    On Large systems, I generally pressurize with perferably dry plant compressed air to the available pressure ( 9 - 10 bar) I then inspect all joints using soapy water to detect leaks (soap bubbles). The pressure should not change more than a few % for 18 -24 hours (overnight) unless there is a large change in ambient temperature.
    Any found leaks are repaired and the system is again pressurized to 9 - 10 bar. Test the repairs. If no leaks are now found, use nitrogen to increase pressure to design working pressure. Repeat the soap test.
    When no leaks are found, purge the air/nitrogen and evacuate the system. This can take more than 24-36 hours. A vacuum test is useful but due to the typically large size & potential for moisture presence, in the ammonia system, it may prove difficult to attain a deep vacuum. Watch your vacuum pump for signs of moisture in the oil.

  3. #3
    Join Date
    Feb 2002
    Location
    Brazil
    Age
    58
    Posts
    26
    Rep Power
    0
    Thanks C. Noseworthy.

    Best Regards.

  4. #4
    muddassarusa's Avatar
    muddassarusa Guest

    Re: Pressure piping test

    Quote Originally Posted by C. Noseworthy View Post
    On Large systems, I generally pressurize with perferably dry plant compressed air to the available pressure ( 9 - 10 bar) I then inspect all joints using soapy water to detect leaks (soap bubbles). The pressure should not change more than a few % for 18 -24 hours (overnight) unless there is a large change in ambient temperature.
    Any found leaks are repaired and the system is again pressurized to 9 - 10 bar. Test the repairs. If no leaks are now found, use nitrogen to increase pressure to design working pressure. Repeat the soap test.
    When no leaks are found, purge the air/nitrogen and evacuate the system. This can take more than 24-36 hours. A vacuum test is useful but due to the typically large size & potential for moisture presence, in the ammonia system, it may prove difficult to attain a deep vacuum. Watch your vacuum pump for signs of moisture in the oil.

    Very good easy and simple explanation.

  5. #5
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: Pressure piping test

    If you are doing additions to existing plant, ensure that when testing with dry nitrogen that you do not exceed system pressure or you may inadvertently add nitrogen into the system through leaking stop valves.

  6. #6
    Join Date
    Dec 2005
    Location
    Norfolk, England
    Age
    66
    Posts
    132
    Rep Power
    19

    Re: Pressure piping test

    This side of the pond we pressure test after blanking off ther safety valves at 32 Bar with Nitrogen for 12 Hrs. when using air / water cooled condensers.

    Arthur.

  7. #7
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Pressure piping test

    Volnei
    For a big system I make a RX inspection of at least 10 % of the pipe welds. All the 10% weld should be good (see Local Code for Pressured System) If there are at least one weld bad I check at least 20 % more

    After I have checked the weld I will perform a neumatic test acording C. Noseworthy have mentioned

    I make vacuon till -700 mmHg a break it with ammonia to close atmosferic pressure and then make a secund vacuom

  8. #8
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Pressure piping test

    Use calibrated & certified pumps and gauges
    X Ray welds as per gwapa post
    Pressure test HP to 65degC refrigerant vapour pressure, LP to 45degC refrigerant vapour pressure.
    Soap solution on welds, flanges ect.
    Stand for min 48 hours = no pressure drop.
    Evacuate to 130 microns or lower, rise no greater than 160 microns in 24 hours.

Similar Threads

  1. Liquid Overfeed Systems
    By US Iceman in forum NH3
    Replies: 151
    Last Post: 08-03-2007, 05:34 AM
  2. dry air for pressure test
    By Lc_shi in forum Fundamentals
    Replies: 2
    Last Post: 23-02-2006, 02:06 PM
  3. pressure test
    By watana in forum Fundamentals
    Replies: 3
    Last Post: 31-12-2005, 09:55 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •