    Receiver on a cap system??



    If you had a syatem which used capillary tubing as a metering device, and you "retain" the receiver ...........what will happen?

    This "engineer" installed a 3/4 hp Le Unite compressor running a small coldroom, using a cap tube, and left the receiver connected

    System goes in deep vacuum, then rises in pressure again. Keeps doing this. He says its moisture, and changed the drier

    I said.........crap, you cant have a receiver connected in line. Take it out

    And I did.........system is charming along now

    Was I right???



  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Was I right???
    Yes...

    A/C and refrigeration systems using cap tubes or short tube restrictors are critically charged systems. One must charge these systems with a relatively exact amount of refrigerant to get them working properly.

    Systems employing receivers are, by definition, non-critically charged systems. These systems require an expansion device which can modulate the flow of refrigerant, e.g., a thermostatic expansion valve.
    Prof Sporlan

  3. #3
    Join Date
    Apr 2001
    Location
    Oklahoma (east central)
    Posts
    9
    Rep Power
    0
    Has our peer above mentioned captube systems are critcle charged. If memory serves me correctly the captube (or a part of it acts as the reciever). Captubes have flash gas in it. At the inlet there is liquid and has rtefrigerant travels through captube refrigerant becomes saturated vapor by the time it exits the captube into the evaporator. HAs the load and ambient conditions change the length of the tube containing the liquid change slightly. This is what makes them so criticle to charge.

    You did the correct thing. Ive seen the same thing. I guess this guy has been out everywhere, leaving in recievers.

  4. #4
    Join Date
    Dec 2001
    Location
    Cincinnati, Ohio, USA
    Age
    63
    Posts
    258
    Rep Power
    23
    Would a drier act as a receiver of sorts?

  5. #5
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Would a drier act as a receiver of sorts?
    It does, of sorts...

    The additional refrigerant the filter-drier holds is available from the manufacturer for those who want to weigh in the exact charge.

    It's unlikely you'll see system operating problems by applying a reasonably sized filter-drier to a cap tube system. Of course, all bets are off if you install a 4 core filter-drier shell to one of these systems...
    Prof Sporlan

  6. #6
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    Drier would not be a receiver because the level of ***** in the drier would not change much. At higher pressure, it might hold a little more *****. A reciever would have to be some kind of variable capacity device. Drier would effect the charge of the system though.

  7. #7
    Join Date
    Apr 2001
    Location
    Tyler, Texas
    Age
    53
    Posts
    12
    Rep Power
    0

    Smile

    Yes take the reciever out. And dont you use very a large drier. If you are going to use the Condensing unit with a reciever change it to a TXV let the system go. We had a system(reachin refrigerator) that 2 tech. had gone out on the system always showed low charge. So i got the call on the weekend. I took the call went out and Found Captube evap which was be feed by a receiver system. the Fix.. Well!! I recovered the system. then valve off the receiver and compressor re-ran the liguid line added the TXV install new drier, and sight glass. Then evacuated the system, used a micro guage to ckeck for leaks. Also found the compressor was r-134a compatable. recharged with r-134a(weighed in, also using sight glass). Last heard from manager, "this box has never been this cold." also some one changed the condensing unit out because r-12 was getting to high...
    Last edited by Preston Roy Powell; 06-06-2002 at 03:35 AM.
    Preston Roy Powell
    www.thinkcool.net

  8. #8
    Join Date
    Jul 2002
    Location
    washington
    Age
    37
    Posts
    77
    Rep Power
    22
    My freezer has cap tubing and a receiver... Im assuming its used to pull a high vaccume on the evaporator for cold temps. am i right?
    one mans trash is another mans treasure

  9. #9
    Join Date
    Apr 2001
    Location
    Tyler, Texas
    Age
    53
    Posts
    12
    Rep Power
    0

    Cool

    THis system is a built in refrigerator that is in a line. Originally it was R-12. The condensing unit didnot have a reciever. Some other company can in and changed the condensing unit which had now has a reciever on it. The system never worked properly. So I cut the cap tubes(2) off the evaporator. ANd Had a distribitor for the evaporator on hand ready to fix problem. Now it refrigerates properly and keeps the compressor at proper temp, plus not a noisy,.. THe Problem is fixed customer happy
    Preston Roy Powell
    www.thinkcool.net

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    My freezer has cap tubing and a receiver... Im assuming its used to pull a high vaccume on the evaporator for cold temps. am i right?
    It is highly unlikely that your freezer has a receiver, and if it does then it shouldn't be there. Whatsmore, that is not the purpose of a receiver. The only thing pulling the pressure down on the evaporator is the compressor.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. System without receiver
    By lana in forum Industrial
    Replies: 9
    Last Post: 28-11-2005, 03:55 PM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •