Results 1 to 4 of 4

Thread: chiller

  1. #1
    brian m's Avatar
    brian m Guest

    chiller



    hi, new to site, just finding my way around.
    the question i have is,, what are the initial findings on a water chiller that has a burst on the plate evaporator.
    i.e would the water be obvious at the start of a problem?,
    would i get any wierd pressure readings or would the compressor fail to start? thanks in advance..



  2. #2
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23
    A burst heat exchanger will give two imediate effects I think. THe first is that there would be no gas in the refrigerant circuit and the sight glass should show wet. Also the compressor will have carried on running until the LP switch made or water reached the compressor so the compressor breaker will trip.
    I hope that this helps

    BritCit_Juve

  3. #3
    Join Date
    May 2002
    Location
    Gloucester UK
    Age
    69
    Posts
    12
    Rep Power
    0
    Brian:Certainly you would have no refrigerant pressure to speak of but I would meg the compressor before starting it and see if you can get an oil sample.I have had them actually spout water when putting on my gauges.You could also pressurize the system and see if you have any positive results on the water side.Cheers Rick

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, If the compressor was a open type water reaching the compressor would not throw the breaker due to an electrical short circuit. The compressor would go out on LP or possibly oil pressure. I have seen systems where you could see an oil water emulsion in the liquid lie sight glass.
    Regards. Andy.
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Chiller
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 08-04-2006, 02:48 PM
  5. closed loop chiller
    By bender in forum Trouble Shooting
    Replies: 8
    Last Post: 02-01-2003, 01:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •