Results 1 to 25 of 25
  1. #1
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Wood Kiln dehumidifier?



    A friend of mine runs a mill shop for wood, he makes kabinets to kitchens, he gets alot of his wood from a friend of his who has a mill so lots of the wood is wet.

    His Kiln thus far is electric run and he's been using home style dehumidifiers, the resualts are good but short lived as the units die off rather fast due to the internal heat.

    I have a couple 6,000BTU units that I think could be built to run as a dehumidifier for his 8*8*20 Kiln. To start the temp inside the Kiln will be: (Will have to get this info again!).

    My plan for ordering the parts was evap, condencer 1 (Inside duct to reheat the air) then Condencer 2, to finaly ensure it was well cooled liquid going back to the TXv.

    Does any one have any tips or sujestions that would ensure good opperation? Will either R-134a or R-22 be sufficient for this opperation, most old dehumidifiers used R-500.

    For the evap I was thinking of just using 3/8 made into a spiraled coil siting inside the duct then a standerd style condencer after it to reclaim the heat, then the condencing unit rather un-modified. I'll be using an oil seperatour to have minimum oil inside the system and keep it at the compressor!



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Wood Kiln dehumidifier?

    I've made many wood killn dryers, even with ambient temperatures of 60°C (140°F)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Wood Kiln dehumidifier?

    Ah K, any design tips or could you help steer me into the right direction? I'm still working on my first heat pump project! lol

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Wood Kiln dehumidifier?

    You only need one condenser in the system, installed just after the evaporator.
    This way, you can mount the unit on 4 wheels.
    The evaporator was mounted vertical and the condensor horizontal above the compressor. This way, the compressor was in the cold stream of the outlet of the evaporator.
    Use a gas with low high pressure (R134a)
    We used R114 in the past for the high ambient temperatures I mentioned (Bitzer compressors)
    Try to evaporate at 0°C and don't be afraid to condens relative high.
    You will need separate heaters - we installed electrical heaters - for the first warming up of the room.
    Once it's running, the compressor will maintain the temperature
    Do you also want to dry oak?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Wood Kiln dehumidifier?

    It sounds a lot like the operating conditions of a heat pump clothes dryer. You'll probably need a special compressor for good results. (You can also try a regular compressor and keep the superheat low.)
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Wood Kiln dehumidifier?

    The equipment Peter is describing is all based on standard components I believe. The special areas are the engineering to make it work and how the system is put together.

    The critical aspect of this is to keep the components within the design application envelope. The operating conditions may be non-standard, but the application of the components is basic.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Wood Kiln dehumidifier?

    Spot on US Iceman, the components are all standard ones.
    Superheat can be held low by a controlled (TEV) injecting liquid in the suction, just before a suction accumulator (sorry NoNickName, liquid strainer )

    Just if you wants to dry oak, then I suggest that you ask to coat the evaporator, especially the bends on the side where they're soldered or use a stainless steel one.

    We've done it and it worked very well by spraying zinc on the bends ( http://www.zinga.be/ ) and repeated this twice a year (the customer did it himself) so that the zinc acts as a sacrifying metal and protects better the copper.

    http://www.ca.uky.edu/agc/pubs/for/for55/for55.htm
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Wood Kiln dehumidifier?

    Quote Originally Posted by The MG Pony View Post
    A friend of mine runs a mill shop for wood, he makes kabinets to kitchens, he gets alot of his wood from a friend of his who has a mill so lots of the wood is wet.

    His Kiln thus far is electric run and he's been using home style dehumidifiers, the resualts are good but short lived as the units die off rather fast due to the internal heat.

    I have a couple 6,000BTU units that I think could be built to run as a dehumidifier for his 8*8*20 Kiln. To start the temp inside the Kiln will be: (Will have to get this info again!).

    My plan for ordering the parts was evap, condencer 1 (Inside duct to reheat the air) then Condencer 2, to finaly ensure it was well cooled liquid going back to the TXv.

    Does any one have any tips or sujestions that would ensure good opperation? Will either R-134a or R-22 be sufficient for this opperation, most old dehumidifiers used R-500.

    For the evap I was thinking of just using 3/8 made into a spiraled coil siting inside the duct then a standerd style condencer after it to reclaim the heat, then the condencing unit rather un-modified. I'll be using an oil seperatour to have minimum oil inside the system and keep it at the compressor!
    Ventilate with that dry alberta air

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Wood Kiln dehumidifier?

    MGPony,just re-read your post: an oil separator isn't needed at all.

    You will have to install a finned evaporator, just a bare coil will not work (exchanging surface far too small)

    I should take R134a, the room needs to run at +/- 40°C (104°F) so this will give you pressures of +/- 16 bar (230 psi) where this will be 22 bar (or 320 psi)

    You need all the heat the machine can gives to maintain the needed high room temperature.

    You doesn't need cool liquid to the TXV, just subcooled liquid.

    This is in fact a very basic machine.

    http://www.nigos.co.yu/nigolux8eng.html

    We installed also additional fans inside the room to increase circulating air volume like this http://www.nigos.co.yu/conddryers.html

    8*8*20 is how big in metric

    R500 gave relative low high pressures, same reason why we used R114
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Wood Kiln dehumidifier?

    Quote Originally Posted by Abby Normal View Post
    Ventilate with that dry alberta air
    BC! Thank you. We most certainly don't have dry air!

  11. #11
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Wood Kiln dehumidifier?

    In SI 2.5M * 2.5M * 6.1M. I was orrigionaly going to have the compressor external to the air stream.

    I have a 2 - 3 Ton scroll as well, set to origionaly use R-22, but with an oil change it may work out well.

  12. #12
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Wood Kiln dehumidifier?

    the room needs to run at +/- 40°C
    In that case, you should be able to use a standard condensing unit and evaporator and just slow down the evaporator fan.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  13. #13
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Wood Kiln dehumidifier?

    Quote Originally Posted by The MG Pony View Post
    BC! Thank you. We most certainly don't have dry air!
    Castlegar is pretty dry, Vancouver Island despite its proximity to the pacific probably would not have much more of a dewpoint than 60F as a worst case scenario

  14. #14
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Wood Kiln dehumidifier?

    winter time it's all dry

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Wood Kiln dehumidifier?

    if you call 85/95% humidity dry.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Wood Kiln dehumidifier?

    85% at -20°C is indeed dry but I know what you mean.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Wood Kiln dehumidifier?

    Hmmm new one to me? then what do they call wet? 100% I think we're swimming at that point! lol

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Wood Kiln dehumidifier?

    If you breath in that air and your mouth our your throat our lungs heats this up to 37°C, then this will dry out your mouth.

    To place it in your example, if you take this cold but humid air and reheat it to the desired 40°C in your kiln dryer, then it will reuslt in an RV of +/- 5% and a very, very low absolute mositure content.

    Perhaps this clarifies a little bit more what I was trying to say. , what I mean, numbers can be so relative.

    Source: Regional average forecasts for Alberta which gave me a minimum temperature of -18°C
    Last edited by Peter_1; 20-01-2007 at 11:13 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Wood Kiln dehumidifier?

    But I am talking about BC, whats all this about alberta?

  20. #20
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Wood Kiln dehumidifier?

    The ALberta comments are my fault, that is where I thought you were from.

    Relative humidity is the most confusing term in HVAC as it is relative to the temperature.

    Example it could be a pea soup fog (100% Relative humidity) and the outdoor temperature was 10C . If you could warm this 'saturated air' to 24C, the relative humidity would have dropped from 100% to less than 42%, yet the amount of moisture in the air would be the same.

    Get temps down to close or below freezing and the air holds very little moisture compared to room air temperature. Ventilating in winter lowers the RH indoors.

    Because you are near the pacific does not make you humid.

    Highest recorded dewpoints in the world are in the Persian Gulf

  21. #21
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Wood Kiln dehumidifier?

    Why I say it is humid as it takes any thing forever to dry via evapouration, at least at ambient temps.

    Your example makes alot of sense after a good nights sleep!

  22. #22
    Steve Coates's Avatar
    Steve Coates Guest

    Re: Wood Kiln dehumidifier?

    Hi,

    I have been also asked to look at replacing a wood drying kiln dehumidifier. The old unit no longer works and is roughly 2ft x 1ft x 1ft in size. I was hoping to copy the old unit for sizes but the small hermetic compressor datails are not visible and the unit runs on R12. The condenser and evap are roughly 1ft x 1ft x 4inches. Can anyone give me some idea of compressor and capillary sizes for this unit if I was to use R134a?

  23. #23
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Wood Kiln dehumidifier?

    When the ambient air is less than 0C, even at 100%RH, and heated to room temp (or higher), it will outperform a dehumidifier.
    Last edited by Gary; 01-02-2009 at 08:30 PM.

  24. #24
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Wood Kiln dehumidifier?

    Here`s an interesting link if anyone needs a new dehumidifier www.humiditycontrol.co.uk/flexisorb.htm

    I`ve been doing some work on one recently, pretty simple idea but effective

  25. #25
    alex.wang's Avatar
    alex.wang Guest

    Re: Wood Kiln dehumidifier?

    Agree with your opinion

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •