    Pressure Equipment Directive



    Hi, what are you all doing regarding the Pressure Equipment Directive, which becomes mandatory in europe from the first of June.
    Also did anyone know that this started from 1999 and that by now we all should be up to speed and ready for phase in.
    Any system with an internal volume above 50 Litres is the cut in point I think for PED, what have you heard?
    Regards. Andy.



  2. #2
    Join Date
    Jul 2001
    Location
    AArhus, Denmark
    Age
    70
    Posts
    7
    Rep Power
    0

    Wink

    The 50 liter depends on the working fluid group and the maximum working pressure (opening of safety valves). We have been working with this directive for quite some time now. Mind you that when you affix a CE mark on your unit, you say that your system is in accordance with all relevant directives. I gues from your note that you know them all allready.

    Alex

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    I think you will find that the directive applies to any system or container that contains a pressure of 0.5bar

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, Frank, yes I had heard 0.5Bar up, this ofcourse includes hermedic compressors, so any system internal volume 50Litres with a pressure above 0.5 Bar. Really anything from a butchers coldroom up.
    Regards. Andy.

  5. #5
    Join Date
    Jul 2001
    Location
    AArhus, Denmark
    Age
    70
    Posts
    7
    Rep Power
    0
    One has to bear in mind that the PED also covers brine systems (because they are above the 0.5 bar limit), allthough the pipes have to be very large before you get in to kat. 1 or 2. The documentation is the same. Many installer forget this fact when they install chillers.
    When reading the PED one realise that the ISO 9000 systems are quite similar. I gues some good things can come out of the implementation once you get through it.

    Good luck

Similar Threads

  1. Pressure Equipment Directive
    By Rob Hat in forum Legal-Business-Marketing
    Replies: 2
    Last Post: 24-11-2005, 11:55 PM
  2. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  3. Pressure Equipment Directive
    By frank in forum Air Conditioning
    Replies: 2
    Last Post: 04-12-2002, 08:31 PM
  4. PED (Pressure Equipment Directive)
    By Steve in forum Technical Discussions
    Replies: 11
    Last Post: 14-12-2001, 04:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •