    Question centrifugal fan



    Good time
    Have you ever paid deep attention to the concept
    of functional curve of centrifugal fans with thin ,
    forward blades such typical one as "NICOTRA" ?
    What happen when this blower works at the same
    static pressure and different air flow rates on the
    constant rpm ?
    thanks s.pirs.


    S.P

  2. #2
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23
    Because the static pressure and external are tightly related I don't think this situation could exsist. The fan is usually selected, along with its motor, belts and pulleys, to meet a set criteria of airflow against static. Lower the static on that match and the airflow will go up and vice versa.

    As an example when a fan is selected to do an airvolume of x against an external static of y but is used against an external static of d the equation is

    resultant airflow R=1/(square root(x*(d/y)squared))

    x and R are m3/s whilest d and y are Pa

    I hope this helps

    BritCit_Juve

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    I agree, I didn't realize that one could maintain the same static (Total static pressure) and change flow rates without resizing the devices that are in the air stream. I am not sure I understand the question.

Similar Threads

  1. York Centrifugal
    By Peter_1 in forum Industrial Compressors
    Replies: 12
    Last Post: 14-08-2005, 01:25 PM
  2. backforward curve centrifugal fan
    By Lc_shi in forum Fundamentals
    Replies: 1
    Last Post: 29-04-2005, 10:35 PM
  3. selection of centrifugal fan
    By watana in forum Air Conditioning
    Replies: 0
    Last Post: 14-09-2003, 04:02 AM
  4. Centrifugal chillers part 2
    By reggie in forum Industrial Compressors
    Replies: 0
    Last Post: 16-05-2002, 09:07 AM
  5. Centrifugal chillers
    By reggie in forum Industrial Compressors
    Replies: 2
    Last Post: 02-05-2002, 07:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •