    can anyone help me with low suction super heat problem 2x sabroes runs 8x diff size room with diff temps units set to cut out at 2.1 bar pm.valve on each room but during night when theres no load unit trips super heats on each room are fine could this be with liquid sitting in lines on start up when one room calling for cooling



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: sabroes

    Hi, John Howie

    Welcome to RE

    Quote Originally Posted by john howie View Post
    can anyone help me with low suction super heat problem 2x sabroes runs 8x diff size room with diff temps units set to cut out at 2.1 bar pm.valve on each room but during night when theres no load unit trips super heats on each room are fine could this be with liquid sitting in lines on start up when one room calling for cooling
    Can you explain this in plain english, please?

    Also can you tell us something more about your compressors, refrigerant, set points, PLC if any and so

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: sabroes

    Quote Originally Posted by john howie View Post
    can anyone help me with low suction super heat problem 2x sabroes runs 8x diff size room with diff temps units set to cut out at 2.1 bar pm.valve on each room but during night when theres no load unit trips super heats on each room are fine could this be with liquid sitting in lines on start up when one room calling for cooling
    Is this a direct expansion system (sounds like that) or a pumped circulation system.


    Probably TEV's not EEV's, wouldn't be uncommon with TEV's especially with low loads and the valves not just selected with this in mind.

    Kind Regards Andy