Results 1 to 5 of 5
Thread: moveing oil to sylinder
-
26-09-2007, 09:49 AM #1
moveing oil to sylinder
hi evry body.
our compressors are carrier 06E type.
in one of our compressor which has been recently overhauled ,we could hear knocking sound in the valve plate (SYLINDER HEAD) during operation.
when we opened the top sylinder head ,there was a lot of oil on top of piston in the cylinder.
could you help me to find the reason.
NOTE: during the normal operation was not oil foaming in oil sight glass.
-
26-09-2007, 11:31 AM #2
Re: moveing oil to sylinder
Hi karimihassan
Can you give some more info about the system this compressor is on. Are there multiple compressors? What is the refrigerant? Is this the original compressor? If so why was it overhauled? Burnout, smash up, inefficient or old age?
Some reasons for oil on piston could be oil rings worn or oil slugging from evap.
Have you removed all heads and inspected valve plates for damage?
-
26-09-2007, 01:20 PM #3
-
27-09-2007, 08:37 AM #4
Re: moveing oil to sylinder
hi guys ,if it has being overhauld it sounds like liquid slugging to me ,i would pumpdown the system and if the noise goes away u would then year a change,
-
27-09-2007, 09:37 AM #5
Re: moveing oil to sylinder
I met this problem once with acopland compressor the cause was the piston rings installed incorrectly the upside down and they were scrapping the oil up instead of scrapping it down.iI hope I could help you.