    alarm shows low pressure



    Hi,
    Thank u first,we have chiller that use in moulding machine,having 4 compressor,with 407 c refrigerant they said its a long time problem that always show in alarm that low pressure,today i saw it that # 3 compressor is the low pressure.My experiences is in Middle east (kuwait)thats why im not pamiliar here in UK.Can i add gas if i found it that less gas?This is air cooled unit.

    Thank u if you will give me an advice
    Cesar/Nottingham



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: alarm shows low pressure

    Too much gas, probably, and too much subcooled. Can you check SH and SC?

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: alarm shows low pressure

    Quote Originally Posted by C Bagtas View Post
    Hi,


    Can i add gas if i found it that less gas?


    Cesar/Nottingham

    No..

    The gas in the system if short will need reclaiming and new adding. If low then the reason why it is low should be established and dealt with.
    We can't just top up system any more because the refrigerants are blends and boil over different temps.

    Cheers taz.

  4. #4
    Join Date
    Aug 2005
    Location
    uk
    Posts
    45
    Rep Power
    0

    Re: alarm shows low pressure

    Quote Originally Posted by NoNickName View Post
    Too much gas, probably, and too much subcooled. Can you check SH and SC?
    Thanks to you no name,i have just told to my manager to send an engineer from manufacturerbec. i cannot add gas,i dont have tools to do reclaiming of gas and charge it.
    Bye and regards,
    Cesar

  5. #5
    Join Date
    Aug 2005
    Location
    uk
    Posts
    45
    Rep Power
    0

    Re: alarm shows low pressure

    Quote Originally Posted by taz24 View Post
    No..

    The gas in the system if short will need reclaiming and new adding. If low then the reason why it is low should be established and dealt with.
    We can't just top up system any more because the refrigerants are blends and boil over different temps.

    Cheers taz.
    Hi,
    Thank you to your response,i have told that to my boss to send an engineer from the contructor of company,bec. they have every thing to do the job,Thanks i have got an idea now.
    Bless you.
    Cesar

  6. #6
    Join Date
    Jan 2007
    Location
    Canada
    Posts
    13
    Rep Power
    0

    Re: alarm shows low pressure

    goof information