    all frozen up



    Hi every one.
    this is my first time so please be gentle. I just install a copeland seimi hermic compressor for a freezer. this is a o&m replacment the old unit had 13# of r22 in it the new unit would only take 8#. the only thing that i changed was the condencing unit. i have bubbles in the sight glass and when i try to add the rest of the charge i get freeze up on the suction side king valve
    my super heat is 12-18deg the system super heat is 40-45deg (temp at the suction king valve) the cabinet is holding a -5deg temp which is what i want.
    am i ok.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: all frozen up

    Hi BooBoo and welcome to the forum.

    You say that you have installed a new compressor then go on to say that you 'only' changed the condensing unit.

    If you changed the condensing unit then perhaps the system charge size has changed.

    Maybe the charge that you took out was 4lbs over weight.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: all frozen up

    If adding refrigerant increases subcooling and causes freezing on the suction side of compressor, then it probably means that the condensing pressure is too low, and now the condensing unit is too big.

  4. #4
    booboo's Avatar
    booboo Guest

    Re: all frozen up

    thanks for the replys. this was a replacement of a blown compressor. ireplaced the whole comdencing unit with the condencer. this was o&m. i found the problem. it was the king valve on the compressor head. it was almost closed all the way. i didn't think to check that because i always use the service valve on the receaver. ifeel very dumb right now, but very happy i found it. again thanks for the replys

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: all frozen up

    Say no more.............

    Glad it is solved.
    Brian - Newton Abbot, Devon, UK