    Would anyone care to offer some spiel on unloaders, the ones fitted on the head part of compressors

    I see them installed on the compressors I work on, but Ive never had to commission one, ie: set the pressure switch settings, etc

    I know they kick in on start up, apart from that Im green on this subject

    Ok........who said I was an ace tech anyway? But Im getting there............. ( with your guys help!!)



  2. #2
    Join Date
    Apr 2002
    Location
    london
    Posts
    70
    Rep Power
    23
    Most internal unloaders in the cylinder head are operated by oil pressure which lifts the suction valve ring plate from its seat via lift pins. Once the valve is seated then the cylinder can seal. If the valve is lifted off its seat then the refrigerant pressure is pumped straight back into the suction line hence no compression.

    The oil pressure which is responsible for the seating of the valve is generally controlled by an actuator which can be adjusted
    by the tension of its internal spring. This in turn moves a floating piston which fires the oil to each individual unloader in stages.

    So the compressor is regulated by back pressure. The higher the suction pressure the more unloaders activated by the actuator.

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Unloader

    Quote Originally Posted by Abe View Post
    Would anyone care to offer some spiel on unloaders, the ones fitted on the head part of compressors

    I see them installed on the compressors I work on, but Ive never had to commission one, ie: set the pressure switch settings, etc

    I know they kick in on start up, apart from that Im green on this subject

    Ok........who said I was an ace tech anyway? But Im getting there............. ( with your guys help!!)
    Usually you will set the unloaders with a pressure switch if they are suction actuated rather than electric, or sometimes have an adjustment screw on the compressor (the Trane 8 cylinder recips have one) You would set the cut in and differential so that your compressor loads at a certain pressure and then unloads as the suction pressure and load reduce. You don't want to flood them and on the other hand you don't want to have them cycling the unloaders on and off every 2 seconds.
    a problem shared is a problem halved

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Unloader

    Another unloading system in starting time is in discharge pipe you have check valve . before that they put one solenoid valve and goes to suction line . In starting time fist it come this solenoid valve one to
    Equalize pressure in low and high side of compressor about 5- 10 sec then compressor comes on in star
    After if goes to delta solenoid goes off.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Unloader

    Another unloading system in starting time is in discharge pipe you have check valve . before that they put one solenoid valve and goes to suction line . In starting time first it come this solenoid valve one to
    Equalize pressure in low and high side of compressor about 5- 10 sec then compressor comes on in star it is on ,After if goes to delta solenoid goes off

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Unloader

    Quote Originally Posted by Abe View Post
    Would anyone care to offer some spiel on unloaders, the ones fitted on the head part of compressors

    I see them installed on the compressors I work on, but Ive never had to commission one, ie: set the pressure switch settings, etc

    I know they kick in on start up, apart from that Im green on this subject

    Ok........who said I was an ace tech anyway? But Im getting there............. ( with your guys help!!)
    hi there mai me at gill@gosheneng.co.il
    i have scanned info on loaders ,trane and carrier
    & copeland, would be happy to send .

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Unloader

    Rest this thread in piece. 7 years old. Must be a record.

Similar Threads

  1. carlyle 5H120 problems
    By old gas bottle in forum Industrial
    Replies: 4
    Last Post: 08-07-2006, 04:32 PM
  2. Unloader Set points
    By KeithCA in forum Trouble Shooting
    Replies: 4
    Last Post: 07-09-2005, 06:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •