We are getting there.
What you are calling the autoload disable is what I believe is a point at above which the Compressor will not load. This is prevent the compressor from overloading at high suction pressures. (The higher the Suction Pressure, the higher the load on the motor.)
The deadband setting is usually with 6-10 KPA.
If this is not a standard control panel made by a manufacturer, you may not have a deadband programed in.
Is this a custom panel, not by the Compressor Manufacturer?