    Suction pressure problem during defrost



    This is my first entry so let me first say hi to all of you. I've been reading a few post here and I've found some valuable info and for that I want to thank you!

    I am working on a freezer running on 404a and I have a few problems. When the unit turns into defrost mode, the suction side pressure doesn't change, it stays at the same pressure as when the compressor is running (10-11 PSIG, which I know is too low for 404 but that's another issue). Can anybody give me a clue as to what to investigate because I don't think this is a normal situation!

    Thanks for the help!



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Suction pressure problem during defrost

    Welcome to the Forum Etienne!
    We need to know a bit more about your system.
    Number of Evaporators, type and size of Compressor, Type of defrost, etc.
    Just on the face of it it sounds like it is not going into defrost mode.
    Is the Evaporator Icing up?

  3. #3
    Etienne's Avatar
    Etienne Guest

    Re: Suction pressure problem during defrost

    I've resolved the defrost issue.

    Compressor is a 1/2HP semi-hermetic, 1 evap, tx valve, receiver and defrost is done by heating elements.

    Now I'm worried about the charge of refrigerant. A suction pressure of 11 PSIG is too low for 404a but since the sight glass is full, I am assuming that the system is not undercharged. Now how can I make sure I have the right charge? Do I just put gas up until I have an appropriate suction pressure?

  4. #4
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: Suction pressure problem during defrost

    Hi etienne,
    are you sure that the sight glass is full, it is possible that when short of gas there is so little in the glass it is easy to assume its full, i would suggest you check its is full by pumping it down and when you reopen the receiver valve watch the glass to see the amount of liquid.

  5. #5
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Suction pressure problem during defrost

    What was the defrost issue?

  6. #6
    Etienne's Avatar
    Etienne Guest

    Re: Suction pressure problem during defrost

    Quote Originally Posted by nh3wizard View Post
    What was the defrost issue?
    a broken relay, simply!

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Suction pressure problem during defrost

    If the problem was always there: too small an orifice, evaporator too small, compressor too big.

    If happened just recently: TXV partially blocked due to moisture or TXV is loosing it's charge.
    But, most important measurement for this: what's your SH?

    Don't search much further for the moment.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.