    Lightbulb VRF Pipework Design

    Morning all,

    Hopefully the correct section.

    I am not 100% on VRF systems and pipe design so hoping someone may be able to assist. I have a piping and wiring diagram so pretty happy on pipe sizing.

    Now, my main concern is linear thermal expansion on 1 1/8" pipe. Will be installing 65 odd meters vertically down a riser (plus the rest of the system) and have done some calcs and would be looking just shy of 100mm linear expansion possibly.

    The bottom of the riser I will then break through into offices running horizontally. Need to maintain flow as best as possible, so no street bends will be installed, all long radius bends, due to longest run being 194m.

    Now, would I best doing the below?

    I'm leaning towards the loop but being 1 1/8" not sure I can get that, wanted expert installers opinions.

    Would I need these loops on the vertical and horizontal runs?

    Capture.jpg

    Many thanks for the help
    Last edited by Stretch79; 09-05-2024 at 09:32 AM.

  2. #2
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    139
    Rep Power
    22

    Re: VRF Pipework Design

    Application Note 2030:
    Thermal Expansion of Refrigeration
    Piping In VRF Systems
    Check this on http://www.mylinkdrive.com

  3. #3
    Join Date
    May 2017
    Location
    Essex
    Age
    44
    Posts
    84
    Rep Power
    8

    Re: VRF Pipework Design

    Hi there, the link won't open

  4. #4
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    139
    Rep Power
    22

    Re: VRF Pipework Design

    Quote Originally Posted by Stretch79 View Post
    Hi there, the link won't open
    https://dropmefiles.com/a9bSa

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: VRF Pipework Design

    Is it 3 or 2 pipe VRF?

    Is this the suction pipe?

    If 3 pipe then the suction will remain suction, where would linear expansion come into it? ( am open to new knowledge btw, this isn't something i'v'e come across except on discharge lines?)
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    May 2017
    Location
    Essex
    Age
    44
    Posts
    84
    Rep Power
    8

    Re: VRF Pipework Design

    Quote Originally Posted by al View Post
    Is it 3 or 2 pipe VRF?

    Is this the suction pipe?

    If 3 pipe then the suction will remain suction, where would linear expansion come into it? ( am open to new knowledge btw, this isn't something I've come across except on discharge lines?)
    Hi Al,

    Believe I've been looking into this too deeply. The pipe will on ever be a suction pipe, other being a liquid, this will not be a discharge line, so I would say I've looked at this wrongly, appreciate the input.

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: VRF Pipework Design

    No bother Stretch, i was scratching my head myself over it as well
    Mostly found in the southern part of this green and pleasant land.