    R407C vs R22



    If I were to change to R407C from R22

    Would the head pressure be higher for R407 then R22
    Would I have to adjust the HP control and the condenser fan cut in switch?

    Is a HP condenser cut in at around 200 psig be adequate



  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Would the head pressure be higher for R407 then R22
    Yes, in the normal condensing temperature range (70°F - 120°F)

    Would I have to adjust the HP control and the condenser fan cut in switch?
    A simple yes or no probably isn't possible without additional information.
    Prof Sporlan

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    When you say changing to R407 from R22 do you mean as a "drop in"?

    This is not possible without an oil change as 407 requires a synthetic oil. If you are talking about an a/c application then yes the compression is normally higher than that of 22 but we have not yet encountered discharge pressures anything like the levels referred to in the press or by word of mouth.

    At evaporating temperatures around 5 deg C you can expect a drop in performance of about 5% but as the evaporating temperature drops to sub zero the performance duty drops off rapidly making this refrigerant unsuitable for low temperature applications.

  4. #4
    Join Date
    Aug 2001
    Location
    NE Lincolnshire, UK
    Posts
    145
    Rep Power
    23
    I have also heard that, in comparison to R22, R407C is more likely to condense out in the wet suction return line, and trash the compressor valve plates.

    We were alerted to this when a compressor manufacturer refused to supply the contractor installing a 400kw A\C plant with the compressors the contractor originally wanted to use, based on the long suction pipe runs.

    Has anyone actually had any experience of this where R22 has been changed to R407C on a big plant?

    Steve

  5. #5
    ashraf Bhatti's Avatar
    ashraf Bhatti Guest

    Re: R407C vs R22

    R22 gas low pressoure is grater then R407C, and high pressore is hier then R 22 gas. please tell me how much difrance between low & high presoures

Similar Threads

  1. P/h chart for R407c
    By Coolie in forum Technical Speculations
    Replies: 4
    Last Post: 29-05-2011, 06:17 PM
  2. R407C to R404a
    By MaDiNfO in forum Air Conditioning
    Replies: 10
    Last Post: 30-07-2006, 09:34 AM
  3. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM
  4. R407C composition
    By Jai in forum Air Conditioning
    Replies: 4
    Last Post: 01-02-2002, 08:59 AM
  5. R407c
    By Mike Hopkins in forum Refrigerants
    Replies: 7
    Last Post: 14-12-2001, 05:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •