Thread: Adding oil
    Nov 2005
    canada
    11
    Adding oil
    Hi to all!
    Just wongdering if it`s possible to add an oil to semi-hermetic compressor (copeland) without reclaiming all the refrigerant. It has an low oil cut out control.
    Jan 2003
    East Anglia
    1,160
    Re: Adding oil
    A bit more info about the compressor might help about the model but there should be no probelm with pumping down the compressor to top up oil. More concerning is WHY you are needing to do this. is there a leak somewhere and have you repaired it or is the oil migrating somewhere, which adding more oil could cause more problems
    fatboy
    Nov 2005
    canada
    11
    Re: Adding oil
    Thanks for a respond! O yea there was a leak, and I foud and repaired it. It`s a copeland 9RS3-0765TFE using R-404. Should I use just a suction line service port or the one where low oil control connected
    Jan 2003
    East Anglia
    1,160
    Re: Adding oil
    I suppose i should in theory say, do a lowside pumpdown and change the drier at the same time but we live in the real world !!!!!
    Fit gauges, close the suction, you may have to overide LP control to get in in a vac. Switch off, use gas in HP side to equalise in positive pressure. Top up oil, vac out and open up and fire her up again.
    fatboy
    Sep 2005
    Australia
    27
    Re: Adding oil
    pump system down it possible , Isolate comp from system ,pump over system or out to cylinder the remander of gas . vac out comp and suck oil in. run vac pump after new oil is in , if you think you may of suck air then open up system , you dont have to change drier that way.
    a fridgies life is that of never quite understanding.
    Nov 2005
    canada
    11
    Re: Adding oil
    Thanks a lot guys. I shoud learn more about compressors construction , I guess.