    Testing for water in NH3



    One of our customers has become concerned with the amount of water present in his system.
    We need to install a new purger, and would like to include a dewatering option.
    The equipment selection is straight forward.
    What remains is to test the Nh3 for water levels in order to estimate the savings of removing it.
    I have found Airgas offers this testing service in the US, but was wondering if anyone has experience in this area. I suspect it would not be practical to do this in the field and laboratory measurements would be required.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Testing for water in NH3

    HI NH3LVR,

    Here is a good article by Ray Ficker at Hansen Technologies.
    http://www.hantech.com/documents/PDF...AmmoniaSys.pdf


    Try this link. Look at page 4.
    http://www.tannerind.com/PDF/green-aqua-amm.pdf

    Here is another link from the same site that has some good general information.
    http://www.tannerind.com/PDF/blue-anhy-amm.pdf

    Here is a little gadget used for the testing from
    Airgas Specialty Products (the old LaRoche Industries)
    http://www.airgasspecialtyproducts.c...cold%20flo.pdf

    There is a lot of information on the Airgas site for ammonia, so be sure to check that out.

    One last possible source is IIAR. Look for...
    Bulletin 108 - Guidelines for: Water Contamination in Ammonia Refrigeration Systems

    It is $30 for a non-member price.

    If you can check the operating suction pressure and the difference between the sauration temperatures that may provide an indication of how far off you might be. The higher the water content, the more of the offset in temperatures will appear.

    Happy reading...

  3. #3
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Testing for water in NH3

    Thanx US Iceman;
    I knew I could count on you!

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Testing for water in NH3

    Always happy to help.

    Let me know how you make out with this affair.

  5. #5
    Join Date
    Nov 2006
    Location
    USA
    Posts
    13
    Rep Power
    0

    Re: Testing for water in NH3

    I too have read Ray's paper on water contamination. I have recently worked with Ray with the installation of Hansen's New Purger Plus. This is a purger that can also remove water. We installed Hansen's first unit. It took a little tweaking here and there but so far so good. If you are in the midwest and would like your ammonia tested for water we will do it for $500 plus travel expenses. Send me a message if you are interested.

  6. #6
    Join Date
    Jan 2006
    Location
    Chicago Illinois
    Posts
    8
    Rep Power
    0

    Re: Testing for water in NH3

    Quote Originally Posted by I LUV NH3 View Post
    I too have read Ray's paper on water contamination. I have recently worked with Ray with the installation of Hansen's New Purger Plus. This is a purger that can also remove water. We installed Hansen's first unit. It took a little tweaking here and there but so far so good. If you are in the midwest and would like your ammonia tested for water we will do it for $500 plus travel expenses. Send me a message if you are interested.
    How is Hansen's purger working for water removal?
    Ray did a presentation for our local RETA and I was interested on how well it works.

    Thanks
    Mark

  7. #7
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Testing for water in NH3

    I believe Parker R/S offers a purger that will remove water in the system, Ill see if I can find the information.

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Testing for water in NH3

    Hi, all

    This is from Hansen

    http://www.hantech.com/documents/PDF...AmmoniaSys.pdf

    good to read

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Nov 2006
    Location
    USA
    Posts
    13
    Rep Power
    0

    Re: Testing for water in NH3

    Mark,

    So far so good. If you have multiple vessels that operate in a vacuum you will need to have a manifold installed that will allow the purger to take liquid from each vessel. This could obviously be done manually or automatically. The purger is designed to take liquid from a single source and therefore requires somenone to select which vessel is to be purged from. I hope this makes sense. PM if you need further details.

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Testing for water in NH3

    Quote Originally Posted by I LUV NH3
    The purger is designed to take liquid from a single source and therefore requires somenone to select which vessel is to be purged from.
    Probably for the same reason you don't manifold all of the condenser purge connections together, heh?

  11. #11
    Join Date
    Nov 2006
    Location
    USA
    Posts
    13
    Rep Power
    0

    Re: Testing for water in NH3

    I am confused by your comment. All purge points are typically manifolded to a common line that is fed the foul gas connection on the autopurger. In the case of the Purger Pluse. The above is true with the exception of the water removal side of things. There is no solenoid valve installed between the purger plus and the low temp liquid line. The low temp liquid line is the line from which the purger plus samples its ammonia and removes the water from. Not the non condensible purge points. If a someone wants to connect multiple vessels to have water removed by the purger plus, then a manifold would be needed and a particular vessel could then be selected to have its water removed. Of course there would be some valving and check valves required to make this work. I have discussed this with Ray and he is planning a revision to adress this for future purgers.

  12. #12
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Testing for water in NH3

    Quote Originally Posted by I LUV NH3 View Post
    I am confused by your comment. All purge points are typically manifolded to a common line that is fed the foul gas connection on the autopurger.
    I am confused as well. I think this is a matter of semantics. Hansen wants all purge points brought in to the purger in one place, but through solenoid valves so the purge points are selectable, according to the paragraph entitled "Foul Gas Piping for Multipoint Purging" on page two of this pdf.


    http://www.hantech.com/documents/PDF/AP003.pdf

  13. #13
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Testing for water in NH3

    Sorry for the too brief comment guys.

    Quote Originally Posted by NH3LVR
    Hansen wants all purge points brought in to the purger in one place, but through solenoid valves so the purge points are selectable
    That's the point I poorly tried to make. It's not the manifold as the problem, but having multiple sources open simulataneously on the manifold.

  14. #14
    Join Date
    Apr 2002
    Location
    Nova Scotia Canada
    Posts
    16
    Rep Power
    0

    Re: Testing for water in NH3

    What I have done is basically made a still. I have installed an oil pot on a high pressure receiver with a heating element set about 20 degrees above condensing. Run a line back to the top of the receiver or condenser. I get the operators to valve of the supply line and drain. Make sure a relief is installed around isolation valves

  15. #15
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Testing for water in NH3

    That's an interesting idea karelsdr. Just like an oil pot. Do you use a similar operating procedure for this too?

  16. #16
    Join Date
    Apr 2002
    Location
    Nova Scotia Canada
    Posts
    16
    Rep Power
    0

    Re: Testing for water in NH3

    Yeah same idea. Just that in this case a heater is needed to keep the ammonia moving so the water(and oil) is left behind

  17. #17
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Testing for water in NH3

    I've used that idea before for an oil still in a large R-22 system, but never thought about using it for water in an ammonia system.

    What kW heater were you using? It would have to be fairly large due to the latent heat of ammonia, or just wait for a longer time.