    R407c



    We have been using R407c lately as a replacement for
    R22. Typically we are cooling water so temperatures are above 5C and we use direct expansion evaporators made by a reputable firm. I understand glide and now it is more important in low pressure drop DX chiller than higher pressure drop brazed plate. Our component suppliers are good with R407c except the evaporator manufacturer. He is asking if we what the vessels sized on bubble point, dewpoint or an average. I would think that the average properties should be used.
    Does anyone know why he would be concerned with this?
    Has anyone else been asked this question?

    Binman54



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: R407c

    Quote Originally Posted by binman54 View Post
    We have been using R407c lately as a replacement for
    R22. Typically we are cooling water so temperatures are above 5C and we use direct expansion evaporators made by a reputable firm. I understand glide and now it is more important in low pressure drop DX chiller than higher pressure drop brazed plate. Our component suppliers are good with R407c except the evaporator manufacturer. He is asking if we what the vessels sized on bubble point, dewpoint or an average. I would think that the average properties should be used.
    Does anyone know why he would be concerned with this?
    Has anyone else been asked this question?

    Binman54
    Until better advised I would say select on bubble point and set up the system using dew point

    Any other views on this

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: R407c

    Surely the bubble point should be used when sizing evaporators as this is the lowest temperature which will give you the evaporating temp you are aiming for as I understand it. If you take an average your actual evaporating temperature will be lower than required. If you are setting up the TEV superheat you will need to set up from the Dew point.

    Ian

  4. #4
    Join Date
    Apr 2005
    Location
    Canada
    Age
    69
    Posts
    23
    Rep Power
    0

    Re: R407c

    Thanks for the response.
    We do use dew point to set up the TX valves.

    Binman54