    Ultra sonic leak detection



    I'm almost regretting this before i start! has anyone seen,used, touched, played with any ultra sonic leak detection gear, we are thinking of investing in the equipment but i dont want to commit funds on the say so of a hot shot salesman.

    A suited gent who works for a mighty intrenational fridge company tells me they are the best thing ever but due to a "technical problem" he was unable to prove it. Any views



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Ultra sonic leak detection

    They are supposed to be the 'bees knees', they are used (or used to be used) by car manufacturers to find leaks in completed car bodies etc.

    Used to use just the listening device without the sound source being used. Found it good at finding leaks due to the sound escaping gas makes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Ultra sonic leak detection

    Hi Clivet and thanks for your PM

    We trialed these devices and yes they are good, but there is a big down side to it.

    For these devices to work it must be completly silent in the area you are working in, take for example even somebody using a sweeping brush can **** the whole thing up let alone normal refrigeration plant running.( the salesman shouted into the test unit and nothing registered but thats not real life).

    We kept 1 just for the workshop when we build custom built condensing units or packs(totally silent area for pressure testing).

    They are not ideal for engineers use in the field, too much background interference.May be worth keeping 1 just for those one off jobs?

    If i remember correctly they are more tuned to detecting sounds at 40Khz if your gas leak is on this frequency ok, but if not your stuufed.

    Kind regards
    Lrac

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Ultra sonic leak detection

    I have one (SDT, Belgium product)since +/ 20 years and I disagree with certain things you Lrac.
    They can be used perfect in a noisy environment. They only pick-up the ultrason frequencies.
    If it's too noisy, then you allways have your headphone.
    Most leaks produce an ultrason noise, so you can even test them while pulling a vacuum.
    But..you find the leaks much faster with an electronic sniffer.

    As Brian said, I bought mine after seeing it on a fair where they demonstrated it on the seal of a car door.
    So they're very good to test the seals on doors of refrigerated rooms. But for that, you need the ultrasonic transmitter.

    It's very often used here in Belgium for the 5-yearly certification test of underground fuel tanks.

    I also have the pick-uop piece to check bearings and flow inside tubes, valves, pumps.

    The device only converts unhearable sounds to a hearable level. That's all.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Ultra sonic leak detection

    An ultrasonic leak detector is an important tool for leak detection. I have a cheaper one that has found leaks that could otherwise not have been pinpointed.

    Here is a typical scenario: You know you have a leak in a large area that you narrow down to a cubic meter or so. But the electronic and soap bubbles fail you. Turn everything off, and put the headphones on, and you will hear a roaring leak immediately. It could be, as it was last time I found one, a small crack on the bottom of the cap tube for an oil failure control. Impossible to find with bubbles, until you know it is there, and then you put your mirror under it and see the soap spray onto the mirror.

    Ultrasonics are also useful for finding large leaks in overhead piping and outdoor units where wind makes electronics less useful. Much of the ambient noise is filtered out, but the more silent you can make the equipment, the more obvious the leak becomes. With my ultrasonic, you can stand 10 feet away and home in on the sound of my finger and thumb rubbing together.

  6. #6
    Join Date
    Aug 2006
    Location
    norfolk
    Posts
    11
    Rep Power
    0

    Re: Ultra sonic leak detection

    hello
    i have used the agramkow saratronic leak detector that uses protec 5 and a sniffer. big bulky and expensive are the main problem. the best unit i have used for manufacturing applications is the inficon unit that can detect any gas, they cost 15k each but you get what you pay for as these will sense down to 1 gram per year

  7. #7
    Join Date
    May 2006
    Location
    Sterling, IL
    Age
    76
    Posts
    13
    Rep Power
    0

    Re: Ultra sonic leak detection

    Face it there are excellent ultrasonics and there are poor ultrasonics. Shop wisely before you buy

  8. #8
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Ultra sonic leak detection

    Hi All,.

    Until a couple of weeks ago i would have said an ultrasonic leak detector was an expensive waste of money. However, i went on a True course a couple of weeks ago and had a play with one and was very impressed. If you have a small leak they are fantastic, especially for them had to trace leaks on evaperators where you may think the evaps gone but its actually a joint.

    Something i need to look into at some point.

    I am also in the market for a megger/RCD tester. Not planning to use it much so not looking at top end stuff, just something that does the job when needed. Plan to go round city electrical/WF and Newey and Eyres in the new year, any suggestions ?

    Regards

    Fatboy

  9. #9
    Join Date
    Sep 2004
    Location
    Swadlincote
    Age
    71
    Posts
    17
    Rep Power
    0

    Re: Ultra sonic leak detection

    I bought one but still prefer OFN

  10. #10
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Ultra sonic leak detection

    Quote Originally Posted by rdocwra View Post
    Hi All,.

    i went on a True course a couple of weeks ago and had a play with one and was very impressed. Fatboy
    Hi fatboy was the training at P&S williams, went on one my self kit didn't impress me that much but made a nice day out.

    Lrac

  11. #11
    Join Date
    May 2006
    Location
    Sterling, IL
    Age
    76
    Posts
    13
    Rep Power
    0

    Re: Ultra sonic leak detection

    Quote Originally Posted by rdocwra View Post
    Hi All,.

    Until a couple of weeks ago i would have said an ultrasonic leak detector was an expensive waste of money. However, i went on a True course a couple of weeks ago and had a play with one and was very impressed. If you have a small leak they are fantastic, especially for them had to trace leaks on evaperators where you may think the evaps gone but its actually a joint.

    Something i need to look into at some point.

    I am also in the market for a megger/RCD tester. Not planning to use it much so not looking at top end stuff, just something that does the job when needed. Plan to go round city electrical/WF and Newey and Eyres in the new year, any suggestions ?

    Regards

    Fatboy


    Unfamiliar with your term RCD. Fluke has a new multimeter out with megger functions can also measure capacitance.

  12. #12
    Join Date
    Dec 2008
    Location
    USA
    Age
    42
    Posts
    57
    Rep Power
    16

    Re: Ultra sonic leak detection

    I've found electronic leak detectors to be superior over the Ultrasonic.. Maybe in a perfect environment they work. I purchased one and regret it.. The only ambient noise a field tech is really going to experience is other refrigeration/ ac units in operation. Electronic Leak Detectors are much better.

  13. #13
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Ultra sonic leak detection

    We had a small RAC that was leaking a few years ago. We brought it back to the workshop for testing as noone could locate the leak on site. We tried bubble leak, ultrasonic detector,electronic leak detector and dye. The dye was showing leaks on 4 evap U bend joints but none of the other detectors picked up the leaks. I have found the dye to work quite well on small self contained systems. The Ultrasonic detectors have probably improved since but I have found a good quality electronic detector to be the best overall. Has anyone tried an electronic CO2 detector? We are looking at trialing this in the factory for testing new units.

  14. #14
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Ultra sonic leak detection

    I have used ultrasonic detectors with mixed result's. With the unit I have used it was impossible o filter out the background noise sufficiently to make the device usable, however when everything is shut down it works well. I only use it as a last resort, electronic and soap bubbles is the way to go.

  15. #15
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Ultra sonic leak detection

    In Spain people are really satisfied with Ultrasonic leak locators. They're actually quite accurate for finding small leaks. But there are other applications, like checking bearings, compressors, leaky valves... etc.

  16. #16
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Ultra sonic leak detection

    Quote Originally Posted by LRAC View Post

    If i remember correctly they are more tuned to detecting sounds at 40Khz if your gas leak is on this frequency ok, but if not your stuufed.

    Lrac
    The gas leak is on freqency of 36 - 40 kHz

  17. #17
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Ultra sonic leak detection

    The ultrasonic leak locators are normally callibrated or tuned on 40Khz, and leaks are between 38 to 42 more or less.
    You can also check bearings malfunctions. On some devices, you can change the frecuency to 25Khz.

  18. #18
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: Ultra sonic leak detection

    Quote Originally Posted by clivet View Post
    I'm almost regretting this before i start! has anyone seen,used, touched, played with any ultra sonic leak detection gear, we are thinking of investing in the equipment but i dont want to commit funds on the say so of a hot shot salesman.

    A suited gent who works for a mighty intrenational fridge company tells me they are the best thing ever but due to a "technical problem" he was unable to prove it. Any views
    I have the Amprobe ultrasonic kit. I have no complaints with it whatsoever. I'm very impressed with it actually. Some patience is required when learning to properly use the instrument though. For evap coils, spray the surfaces with water first. The bubbling noise is unmistakable, and will allow detection of leaks down to hundredths of an ounce per year (formicary corrosion).

    There are times when electrical interference, or even insect interference, is too great to use it, but that isn't a good reason to condemn the instrument. No method is 100%. Pressure testing only tells you whether there is leak, but doesn't pinpoint the leak for you. Electronic sniffers don't work when there's a breeze, and cannot always pinpoint the source even though it detects the leak. Bubble solution can only be used to check exposed portions of the system, and can blow off of the leak. UV dye is actually the most consistent method in my experience, but requires a return visit, and possible callback due to excessive refrigerant loss before the return visit.

    It's good to have an assortment of methods available, and FWIW the ultrasonic is my favorite instrument/method of the bunch. It's the first thing that I pick up.

  19. #19
    worldb's Avatar
    worldb Guest

    Re: Ultra sonic leak detection

    I use the UL101 Ultrasonic Leak detector. The difference between this and others I've seen is astounding. No background noise and you don't have to adjust the sensitivity. I understand NASA uses it for vacuum leaks in space. The only problem is laminar flow leaks (no ultrasound), in which case a sniffer must be used, but the UL101 is much easier and more reliable in noisy environments, wind, etc.