    residue R404a



    Hello, experts
    I use for work R404A from cylinders.
    Each cylinder contain 10.9 kg of refrigerant.
    In liquid phase its components R125 / R143a / R134a is in ratio 44% / 52% / 4%
    When I charge refrigerator ,
    amount and pressure of refrigerant in the cylinder will decrease ,
    and once some components will vaporize in cylinder,
    and ratio between components get broken.
    So a substance in the cylinder will not be R404a.

    In view of the aforesaid let me ask some questions:

    How much kg of refrigerant I can take from cylinder ?
    What should I do with residue blend ? Can I use it for charging?

    Thanks for any advice



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: residue R404a

    Quote Originally Posted by tralex View Post
    How much kg of refrigerant I can take from cylinder ?
    What should I do with residue blend ? Can I use it for charging?

    Thanks for any advice
    Hi Tralex

    With all blends you should be charging systems with liquid and not vapour from the bottle. The vapour in the bottle will always be their unless you put the bottle in a freezer each time before use(and then you'll still get vapour).

    None of us can do anything about the gas % mixture in the vapour and so liquid charging is the only way to try and get the full % mix out.

    Kind regards
    Lrac

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: residue R404a

    LRAC is correct, and for your last question you should not use more than 90% of weight of the refrigerant content.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: residue R404a

    Quote Originally Posted by NoNickName View Post
    LRAC is correct, and for your last question you should not use more than 90% of weight of the refrigerant content.
    Unless you are putting the whole cylinder charge into the same circuit.

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: residue R404a

    Quote Originally Posted by frank View Post
    Unless you are putting the whole cylinder charge into the same circuit.
    No, since part of the gas will remain in the cylinder anyway. The minimum pressure in the cylinder will be the suction pressure.

  6. #6
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: residue R404a

    Use R507 (AZ50)....no worries then as its an Azeotrope.

  7. #7
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: residue R404a

    Walmart, Winn-Dixie, Publix use R404a as their HFC. This covers about 75% of the supermarkets in the Southeast USA. It cannot be all that bad.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: residue R404a

    Electrocool is right. 507 is much better than 404 and it doesn't have the problem of oil carry over.

  9. #9
    Join Date
    Jul 2005
    Location
    Belarus
    Age
    51
    Posts
    25
    Rep Power
    0

    Re: residue R404a

    Thank you gentleman.

    How you recovery residue refrigerant?

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: residue R404a

    Quote Originally Posted by tralex View Post
    Thank you gentleman.

    How you recovery residue refrigerant?
    You don't. Just close the valve and return the cylinder to your supplier.

  11. #11
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: residue R404a

    Quote Originally Posted by tralex View Post
    Thank you gentleman.

    How you recovery residue refrigerant?
    Pump the system down with the cylinder attached and draw the cylinder pessure down to the lowest you get when pumped down (about 0.2barg).

    Should do the trick. any lower and the thing would be on a vacuum.

    Cheers taz.

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: residue R404a

    Quote Originally Posted by NoNickName View Post
    No, since part of the gas will remain in the cylinder anyway. The minimum pressure in the cylinder will be the suction pressure.
    Exactly the same even if you charge as a liquid

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: residue R404a

    Quote Originally Posted by frank View Post
    Exactly the same even if you charge as a liquid
    No. The equilibrium pressure in the cylinder is different than the suction pressure. If the cylinder is warm, than the pressure in the cylinder is higher than suction.

  14. #14
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: residue R404a

    Quote Originally Posted by NoNickName View Post
    No. The equilibrium pressure in the cylinder is different than the suction pressure. If the cylinder is warm, than the pressure in the cylinder is higher than suction.
    So are you saying that the vapours left in the cylinder following liquid charging are in proportion to the constituant parts, but are not in proportion when charging a full cylinder as a vapour?

  15. #15
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: residue R404a

    Quote Originally Posted by frank View Post
    So are you saying that the vapours left in the cylinder following liquid charging are in proportion to the constituant parts, but are not in proportion when charging a full cylinder as a vapour?
    No, I don't. Actually I use the refrigerant down to the very last drop. My habits have nothing to do with good practice, though.

  16. #16
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: residue R404a

    what if you fire a bit o nitrogen in there and charge only liquid? Then technically all the refrigerant aut to be forced back in only as liquid phase due to artificial pressure the nitrogen induces. Thus you should get no fractioning occurring.

  17. #17
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: residue R404a

    Electrocool is right. 507 is much better than 404 and it doesn't have the problem of oil carry over.
    Is this documented, or just an opinion? The refrigerants are so similar, I am surprised at this observation.

  18. #18
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: residue R404a

    Quote Originally Posted by Dan View Post
    Is this documented, or just an opinion? The refrigerants are so similar, I am surprised at this observation.
    What do you mean by documented? We've built chillers with both refrigerants, if it can be considered documentation, yes it is documented