    compressor starter




    I have never seen this design. Any comments?


    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: compressor starter

    It looks like a single phase CSR with split winding. Rotative hermetic compressors from Sanyo or other brands have a similar starter.

  3. #3
    Join Date
    Jan 2006
    Location
    UK
    Posts
    53
    Rep Power
    19

    Re: compressor starter

    It’s a single phase, capacitor motor starter. On first switch-on, there is a voltage appearing across the 4K7 resistor and this voltage switches on the triacs (the two triangles): they act like a switch and the 160uF capacitor, in the start circuit, is in operation. The motor starts with both windings in circuit. The voltage quickly falls as it leaks away through the 1uF capacitor and the triacs switch off. The motor now runs on the run winding only. It’s a solid state equivalent of the mechanical switch fitted on the motor shaft that takes out the capacitor as the motor speeds up.

  4. #4
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: compressor starter

    Looks like time to buy some parts and test it out (modifying it as needed). I have everything except the 0R1 resistor. I was looking for a solid state circuit to replace a worn out compressor start relay.
    Only concern is that the triac might fire near the peak for each cycle during starting, thereby causing electrical stress.

    I think I'll add a small choke (or resistor) between the triac and start capacitor along with a 5uF motor run capacitor from S to R to "soften" the surges.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  5. #5
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: compressor starter

    I just built the circuit and it works fine. It even worked for a "hot restart".