    Diplomat APM6842 - not cold enough



    hi,

    I'm just after a bit of advice please, to bin or attempt a fix.

    I have a Diplomat - APM6842 fridge freezer, its part of a fitted kitchen behind a door. Its about 4.5 years old so should still work I recon.

    Recently its stopped cooling the fridge, it remains at a steady 12 degrees, so lots of milk and food going off. Er'indoors isn't happy at all with me for not fixing it yet

    Twiddling the thermostat seems to make no difference. The freezer is at -11 degrees.


    From reading some of the other posts and my limited knowledge it looks like the thermostat or a loss of gas? Anyone got any bright ideas?

    I had a look at the thermostat, it seems the metal wire dissappears into the side of the unit, so how on would one replace this? Is there some way of threading a new one through and connecting it at the other end??? (does the metal wirey thing connect at the other end somewhere inside the fridge?)

    Also I contacted a spares company (speedyspares I think they were called), they told me a new stat would be nearly £60, blimey oh riley!!!! Is this a realistic price, sounds very steep to me.

    Final question, is a Diplomat APM6842 the same as a Whirlpool APM6842??

    Thanks in advance for any wise words. I'll owe you one!

    Chedz



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Diplomat APM6842 - not cold enough

    Try defrosting the freezer section completely and then retesting setting the thermostat to it's middle setting.

    Also make sure the doors close properly.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Nov 2006
    Location
    Hampshire
    Age
    50
    Posts
    7
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    Hi,

    we tried that, complete defrost and yes the door is shutting tight. Could it be the thermostat do you think?

    Thanks again
    chedz

  4. #4
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Diplomat APM6842 - not cold enough

    Hi Chedz,
    Yes it appears that Diplomat is same as Whirlpool APM6842. Code number should be 8539755150070/1/2 i.e.ending 0, 1 or 2.

    Correct thermostat code is Whirlpool 5031684765157
    suggested retail 31.69 .
    As the unit is built in to a fitted kitchen has it got enough ventilation and can it get rid of heat? You might have to pull unit out to check to see if compressor is running and then stopping due to overheating. Thermostat is often go/no go. You might want to test refrigeration circuit by bypassing thermostat so that compressor runs continuously.....fridge and freezer should then pull down if all OK with cooling side.
    Unit runs on R600 isobutane.
    Hope this helps.

  5. #5
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Diplomat APM6842 - not cold enough

    You might want to test refrigeration circuit by bypassing thermostat so that compressor runs continuously.....fridge and freezer should then pull down if all OK with cooling side.
    May I just add (for the info of other techs), this method works in every case I have tried..... apart from one.

    A few years ago I was having a problem with a firdge/freezer. When I by-passed the stat everything worked OK, but when left with stat in place the fridge section cooled OK but the freezer hardly worked at all.

    All pointed to stat being 'out of range' and cutting out far too soon. Tried other stat, same problem.

    System was on R600, so fresh gas was put in. Problem remained. I eventually found the fault, inside the freezer section there was a connection for the fridge evap. This had a restiction in it, chopped out bad bit and reconnected, put fresh gas in and all worked well.

    Moral of the story..... always be aware...LOL

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  6. #6
    Join Date
    Nov 2006
    Location
    Hampshire
    Age
    50
    Posts
    7
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    Hi again, thanks for the further info, much appreciated. I'll have a go at bypassing the stat. I tried this once before on a fridge. I used an allen key tapped to a wooden spoon just to be safe. Luckily I did this as whatever I shorted out was live, made a massive flash and melted my allen key.

    Could someone give me a tip on how to bypass the stat without killing myself please?

    Thanks again
    Chedz
    chedxz

  7. #7
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Diplomat APM6842 - not cold enough

    Quote Originally Posted by chedz View Post
    Hi again, thanks for the further info, much appreciated. I'll have a go at bypassing the stat. I tried this once before on a fridge. I used an allen key tapped to a wooden spoon just to be safe. Luckily I did this as whatever I shorted out was live, made a massive flash and melted my allen key.

    Could someone give me a tip on how to bypass the stat without killing myself please?

    Thanks again
    Chedz
    chedxz
    Do not under any circumstances work on the fridge live. Get access to the plug and pull it out to isolate, don't even trust the switch. Unplug the fridge first.
    If the frezer is working but the fridge is not then it indicates somthing other than the stat. Ensure the fridge freezer has only one stat controling it. If it has only one stat and the freezer is working then the stat is ok. That then points to either the comp not pumping correctly or the gas charge being wrong.

    Personaly I think you need to get someone to look at it.

    Cheers taz

  8. #8
    Join Date
    Nov 2006
    Location
    Hampshire
    Age
    50
    Posts
    7
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    thanks for the warning, i'd like to isolate the fault as best I can before calling for backup, I'd hate to pay a fortune for someone to come and change the stat when I can do this myself.

    Regarding the stat, if the stat was ok, wouldn't the warm fridge result in the cooling being permanently on and the freezer being very cold indeed, -11 doesn't sound that cold to me.

    If someone can advise how to bypass the stat I'll give it a go, if that doesn't prove anything I'll call in an expert.

    Cheers

    Chedz.

    my tea tastes funny....oh...the milks off again

    edit: forgot to say, I won't hold anyone responsible if I fry myself. I promise to be careful.
    Last edited by chedz; 17-11-2006 at 04:41 PM. Reason: added disclaimer

  9. #9
    Join Date
    Nov 2006
    Location
    Hampshire
    Age
    50
    Posts
    7
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    anyone able to either:

    1. explain briefly how to bypass the stat.
    2. suggest where to get a new stat: Whirlpool 5031684765157

    Thanks a lot

    Chedz

  10. #10
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Diplomat APM6842 - not cold enough

    Quote Originally Posted by chedz View Post

    Regarding the stat, if the stat was ok, wouldn't the warm fridge result in the cooling being permanently on and the freezer being very cold indeed, -11 doesn't sound that cold to me.

    If someone can advise how to bypass the stat I'll give it a go, if that doesn't prove anything I'll call in an expert.

    Cheers

    Chedz.

    .

    I do not think the stat is faulty. If the thing is running and the frezzer is only at -11 then you have other problems.

    They could be

    1 A faulty comp that is not pumping correctly.
    2 A partial blockage in the system that is not alowing enough refrigerant to flow round the system
    3 A refrigerant leak that has caused some of the gas to escape and therfor there is not enough gas left.
    All of those faults unfortunatly need the attention of somone with the right tools and equipment to check your fridge.

    Cheers taz.

  11. #11
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Diplomat APM6842 - not cold enough

    Is there a FAST FREEZE switch on the freezer? That should run compressor and lower temperatures. Is thermostat set to coldest ....Number 7 not number 1.

  12. #12
    Join Date
    Nov 2006
    Location
    Hampshire
    Age
    50
    Posts
    7
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    I kinda ignored the advice above and went ahead and fitted a new stat, it now works perfectly. I compared the performance of the old and new stats, the old one did switch at the right temp, but compared to the new one it wasn't a clean contact, still reading 440ohms. somehow this must have been effecting the running of the comp...perhaps....what do I know.
    Thanks for the help, I'm off for a nice cold glass of milk now.
    cheers
    Chedz


    (unqualified Refrigeration Engineer - 100% sucess rate on fixes though )
    Unqual

  13. #13
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Diplomat APM6842 - not cold enough

    Quote Originally Posted by chedz View Post

    what do I know.
    Thanks for the help, I'm off for a nice cold glass of milk now.
    cheers
    Chedz


    (unqualified Refrigeration Engineer - 100% sucess rate on fixes though )
    Unqual

    What do we all know eh?
    Good news that you got it going and hopfuly at a reasonable price

    Cheers taz.

  14. #14
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Diplomat APM6842 - not cold enough

    A bad connection would cause the compressor to take exess current and cut out on overload.

    Glad you got it sorted though, thats the main thing.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  15. #15
    Join Date
    May 2007
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    Hi, I have the Diplomat AMPM6518. It is recently hovering around 8-10 degrees. Sometimes though it can dip to 3-4 degrees.

    I have the thermostat set on 7 (max) and overnight recently it doesn't seem to be cooling from around 8 degrees.

    Can anyone tell me:

    1. What the fault is likely to be?

    2. How to fix it?

    I am a novice when it comes to fridges so instructions on how to access relevant parts would be handy. Many thanks.

  16. #16
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Diplomat APM6842 - not cold enough

    Scooter.....cannot find APM6518....only APM6528. Whats the 12 digit code number (starting 85....)

    Is this a Fridge or a Fridge Freezer? Is it supposed to be Frost Free with circulated air (a fan)?

    Need more info

  17. #17
    Join Date
    May 2007
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    It might be quite old. Its a built in fridge. There's no number beginning with 85. It's an APM6518 Type: HTI2121 Art No: 5954442. Its bascially got a freezer box at the top and fridge. Its a compressor type fridge...And it was made in Slovenia not China which must mean its old. It was in the house when we moved in last year.

  18. #18
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Diplomat APM6842 - not cold enough

    Hi Scooter, my info is not showing any model with that info. As its 'built in' my first thought would be to pull it out and check all the ventilation holes are clear. If unit can't get rid of heat, the compressor might be overheating.

    When unit is pulled out, check to see if compressor runs for long periods or cycles on/off frequently. Is compressor quiet or noisy?

    Have you defrosted the icebox? Fridge won't get properly cold with a thick layer of ice on ice box.

    When you've finished defrosting, switch unit back on and close door....after 15 mins or so check the 'frost line' on the evaporator/icebox. The 'lines' on the icebox are 'tubes' thru' which the refrigerant flows...by running your finger along the tube you should reach a point where the frost stops. The frost line should reach along most of the pipe. If its only short and doesnt get longer with time then the system is probably short of refrigerant.

  19. #19
    Join Date
    May 2007
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: Diplomat APM6842 - not cold enough

    Hi, I've now pulled out and checked everything. The compressor works but seems to be unreliable. Sometimes the fridge is at almost zero (ice in yoghurt stuff), other times it's hovering around the dangerous 10 degree mark. Turning the thermostat on and off seems to activate the compressor. Does this mean my Thermostat is buggered and how and where would I go about replacing?

  20. #20
    cableguy's Avatar
    cableguy Guest

    Cool Re: Diplomat APM6842 - not cold enough

    Hi Chedz, i have the same prob. with my diplomat apm 6842, freezer perfect/fridge sitting at minus 10 deg.celcius/beers not cold enough/i found that the air flow is not sufficient, so i have cleared the obstruction, but it is still the same/fridge/freezer 3.5 yrs. old maybe i should get a new stat like you did! was it easy to fit in place??
    Quote Originally Posted by chedz View Post
    I kinda ignored the advice above and went ahead and fitted a new stat, it now works perfectly. I compared the performance of the old and new stats, the old one did switch at the right temp, but compared to the new one it wasn't a clean contact, still reading 440ohms. somehow this must have been effecting the running of the comp...perhaps....what do I know.
    Thanks for the help, I'm off for a nice cold glass of milk now.
    cheers
    Chedz


    (unqualified Refrigeration Engineer - 100% sucess rate on fixes though )
    Unqual

  21. #21
    Nick1313's Avatar
    Nick1313 Guest

    Re: Diplomat APM6842 - not cold enough

    Hi mate could you do me a big favour? I changed the stat on my f/f but while the stat was on the table my son felt he was helping and pulled the wires out of the plastic block which plugs into the stat, could you please take a look at yours and tell me which colour wire goes to what. Cheers mate Nick

  22. #22
    Steve-T's Avatar
    Steve-T Guest

    My Diplomat APM6528 keeps alarming

    The alarm on my built-in Diplomat APM6528 keeps alarming :-

    1) The door seals are working fine.

    2) There is no obstruction of air-flow underneath, behind or above the unit.

    3) The freezer works and is not full of ice + the door shuts.

    4) Ice forms and then melts on the rear inside plate, as it always has done.

    5) Its currently set at 4 degrees and is operating at 4 degrees, though this does go up a bit to 6 or 8 degrees. But the alarm sounds at 4 degrees.

    6) Its not over or under full

    7) The meat chiller compartment is fitted and is switched on at the control panel.

    8) Its 2 and bit years old, having replace the previous one which failed - can't remember why.

    Could the sensor be faulty and is there any way of testing it.

    Any other advice welcomed. I have been adviced to have it re-gassed. Is this viable, can it be done on site and is it more cost effective than paying out for a new fridge.

    Many thanks,

    Steve

  23. #23
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: My Diplomat APM6528 keeps alarming

    How you measured your temperatures?

  24. #24
    Steve-T's Avatar
    Steve-T Guest

    Re: Diplomat APM6842 - not cold enough

    I'm using a Brannan stand alone fridge thermometer. It has just measured 2 degrees c in the chiller box.

  25. #25
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Diplomat APM6842 - not cold enough

    What temperature is in the freezer?

  26. #26
    Steve-T's Avatar
    Steve-T Guest

    Re: Diplomat APM6842 - not cold enough

    The freezer is at -20 degrees

  27. #27
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Diplomat APM6842 - not cold enough

    I am not familiar with these fridges, but I presume that alarm is triggered by faulty alarm sensor or alarm thermostat or relay which drives alarm. But I also may be wrong.

    Based on your temperature readings fridge doing his job and re-gassing isn't needed.

  28. #28
    Gerry36's Avatar
    Gerry36 Guest

    Post Re: Diplomat APM6582 - alarming

    Hi I have a 6528 with the same problem, alarming all thetime, I have had the electronic module changed, still the same, The unit is insured with DOM/GEM they are now saying there is nothing more they can do, so the fridge must be replaced,but as its over 5 yrs I will have to pay most of costs, the fridge is working perfectly, temps are spot on, is there another senser for the alarm, other than the one for the fridge temp

  29. #29
    joescotland's Avatar
    joescotland Guest

    Re: Diplomat APM6842 - not cold enough

    hi
    how do I replace the stat on my Diplomat APM6842? I can't see where where I can disconnect it.
    Thanks

  30. #30
    dan_karen's Avatar
    dan_karen Guest

    Re: Diplomat APM6842 - not cold enough

    Hi I am having a similar problem with the same model but view my problem as worse than others because my beer is just not cold enough.

    Symptoms, Freezer is OK about -18, compressor appears fine with adequate ventilation yet fridge seems to work one minute and not the next, the coldest temperature I seem to achieve is about +7, yes +7 not an acceptable temperature for beer.

    Today I followed advice from this thread and tested the thermostat which is opening and closing the circuit but I am not convinced this is happening at the right temperature. Is it fair to say the thermostat can work one minute and not the next and if faulty will not necessarily cool the fridge enough as it may close the circuit at the wrong temperature, or if the stat is faulty should I also be see symptoms in the freezer which for me is all OK?

    Thanks in advance to anyone who offers advice.
    Dan

  31. #31
    badtoad66's Avatar
    badtoad66 Guest

    Re: Diplomat APM6842 - not cold enough

    I too am experiencing the similar / same symptoms with my APM6842 and would like to bypass the thermostat to rule it out and would ask if anyone could tell me how to go about this and which wires to bridge etc in order to do it. I have stripped the stat out and tested it in open air at 20 degrees and then placed it in the freezer to see if there is a change in the switching which resulted in no change. Prior to removal the fridge was at about 9 degrees and i could here the stat click when it passed number 6 on the dial. Your thoughts please.