    Whats the correct procedure for R22



    Hi guys
    Could someone explain the correct proceedure for filling up an A/C unit with R22?
    Ive got an experimental rig in my workshop, but I cant get the R22 into it! Ive tryed it as a liquid and a vapour and still no go. Does it have to be forced in with a pump or recovery unit?
    Any help would be appeciated.



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Whats the correct procedure for R22

    R22 should make no difference whether it goes in as liquid or vapour as far as the gas in concerned.
    However you do not want to be putting in loads of liquid straight into the compressor.

    depending on the size of the unit, put in some liquid up to half system capacity and give it time to settle/burn off (1 min) then start the system up and continue to top up with vapour. If you have a quick charge attachment then you could go all the way on liquid but if you havnt filling up with liquid straight into the pot when its running will kill it

    Regards

    Fatboy

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Whats the correct procedure for R22

    Have you evacuated the system first ?

    Silly question but are the valves open, is the Schraeder blocked.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    May 2006
    Location
    Cwmbran in South Wales
    Age
    53
    Posts
    18
    Rep Power
    0

    Re: Whats the correct procedure for R22

    I can only get about 50 grams in.
    You say run the unit when aprox 50 %-Is it ok to run the unit without a full charge in it?
    Can R22 be pushed in via a recovery unit?
    I have vapour at the service valve - just seems like very little goes into the system

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Whats the correct procedure for R22

    can you give us any more details about the a/c unit.

    50 grams seems VERY low, even at static pressure you should get more than that in.

    I would have to aggree with Brian, something is seriously wrong here, once vac'd the system would proably take 50 grams to get it back to 0 psi again let along a static charge

    Any more details, system type, make/model, displayed charge weight

    Regards

    fatboy

  6. #6
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Whats the correct procedure for R22

    Quote Originally Posted by Brian_UK View Post
    Silly question but are the valves open, is the Schraeder blocked.
    I think your guage lines are blocked check the rubber seals are not collapsed and the depressers are all ok.

    regards
    Lrac

  7. #7
    Join Date
    May 2006
    Location
    Cwmbran in South Wales
    Age
    53
    Posts
    18
    Rep Power
    0

    Re: Whats the correct procedure for R22

    Ive checked the lines- I have gas as far as the service valve- shreader valve appears to be working fine also.
    valves are deff open!
    Ive checked all the obvious stuff, but as Ive not dealt with R22 before- I thought Id ask u guys if it needed something else....

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Whats the correct procedure for R22

    R22 apart from its makeup is just a refrigerant just like the others, nothing special so don't blame the R22 for not going into the system.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Re: Whats the correct procedure for R22

    Quote Originally Posted by cold as ice View Post
    Ive checked the lines- I have gas as far as the service valve- shreader valve appears to be working fine also.
    valves are deff open!
    Ive checked all the obvious stuff, but as Ive not dealt with R22 before- I thought Id ask u guys if it needed something else....
    May we ask what you have dealt with??

    Cheers

    Richard

  10. #10
    Join Date
    May 2006
    Location
    Cwmbran in South Wales
    Age
    53
    Posts
    18
    Rep Power
    0

    Re: Whats the correct procedure for R22

    Ive mostly dealt with R410A.

  11. #11
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Whats the correct procedure for R22

    One question...what level of tech background do you have?

    Ken

  12. #12
    Join Date
    Jun 2006
    Location
    USA
    Posts
    204
    Rep Power
    18

    Re: Whats the correct procedure for R22

    I have had the schrader valve fail to depress adequately for charge to flow. I've seen it on new hose sets and on new schrader valves. The manifold gauge goes up like normal through leakage but then no gas flows through afterwards.

    I've seen the same thing with a line tap schrader kit. After a few minutes and after considerable charge went through, rubber parts inside swelled and no further gas would flow through the valve either direction.

    With lines hooked to the low side, you should be able to get enough gas in with the system off that the gauges will respond when you power the unit up. Then the pressure will drop in the suction line and allow metering in the rest of the charge.

    Where are your gauges connected?

  13. #13
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Whats the correct procedure for R22

    Quote Originally Posted by cold as ice View Post
    Hi guys
    Could someone explain the correct proceedure for filling up an A/C unit with R22?
    Ive got an experimental rig in my workshop, but I cant get the R22 into it! Ive tryed it as a liquid and a vapour and still no go. Does it have to be forced in with a pump or recovery unit?
    Any help would be appeciated.

    If you need to ask that question you realy do need to ask yourself should I be working on this system at all

    Cheers taz

  14. #14
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Whats the correct procedure for R22

    I've seen the same thing with a line tap schrader kit. After a few minutes and after considerable charge went through, rubber parts inside swelled and no further gas would flow through the valve either direction.
    I had something like that happen with a can tap. Once the static charge (of R134a in my case) slowly went in, I closed the high side gauge valve and started the system. It took a long time to put 12oz of R134a into the unit. I decided to close the low side gauge valve, turn the can upside down, and carefully open the valve again. The can tap iced up, indicating a restriction. After I used up the can and disconnected the hoses, I took the can tap apart and found a deformed rubber valve seat. I already have valves on my gauges, so I just took the seat out. It should work much better the next time I use it!
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Whats the correct procedure for R22

    Indeed, Long as there is oil the thing can run! you won't get any cooling and will heat the compresser nicely with no gas but it will run happily like this for up to 2 minutes (More then enough to charge gas into to).

    As Mr said you ARE doing it via low side right? and have don a full vac? & Leak tested?

    Being you are in the UK are you aware of the curren't laws pertaining to R-22?

  16. #16
    Join Date
    Jun 2006
    Location
    Ireland(ROI)
    Age
    44
    Posts
    28
    Rep Power
    0

    Re: Whats the correct procedure for R22

    Does the R22 container seem unusually light???
    This may be due to container emptyness.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Whats the correct procedure for R22

    The NRV in the cylinder is blocking perhaps?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Aug 2006
    Location
    Philippines
    Age
    52
    Posts
    7
    Rep Power
    0

    Re: Whats the correct procedure for R22

    Hi! I'm new this stuff. If everything goes okay the way you charged as far all the suggestion you followed. It might be the problem is the compressor - loss compression perhaps or charging at low atmospheric pressure.
    That's all I could share

  19. #19
    Join Date
    Jun 2006
    Location
    USA
    Posts
    204
    Rep Power
    18

    Wink Re: Whats the correct procedure for R22

    Quote Originally Posted by leftjobrunning View Post
    Does the R22 container seem unusually light???
    This may be due to container emptyness.

    Sounds like a typical eBay purchase...

  20. #20
    Join Date
    Jun 2006
    Location
    Arizona
    Posts
    39
    Rep Power
    0

    Re: Whats the correct procedure for R22

    Do you have both high and low side gauges attached? Is there any heat transfer occuring when you are operating the system? I would suggest using a core removal tool to remove the schrader core and then attaching your gauges to the tool. Beyond that we would need more information regarding your system and symptons occuring.