It ocurred again today. It seems that mostly having condemned a TEV, that upon removal of the valve from the system, that often the external equalizer port of the valve is oil logged.
Is this observation a CAUSE of malfunction, or a SYMPTOM of the malfunctioning or misapplied component? .
I've conditioned myself to the point that when I open the equalizer connection and oil squirts all over me, that I am confident that my diagnosis is on the mark. And vice versa, the absence of oil in the TEV eq. port (might) cause me to further evaluate a system, aside from any concerns regarding TEV operationLast edited by herefishy; 21-03-2002 at 06:24 PM.
-
21-03-2002, 11:52 PM #2Is this observation a CAUSE of malfunction, or a SYMPTOM
Say we have a situation where the TEV is starving, and oil can trap in the equalizer line and get underneath the power head, either by poor equalizer piping or reverse cycle hot gas defrost. The oil will be essentially at evaporating temperature, and it can cool the head down causing the valve to starve. This is particularly a problem with a TEV having an MOP type charge, e.g., Sporlan 'ZP', as these charges will migrate to the head under these conditions. But even if the TEV doesn't have an MOP charge, the oil underneath the power head still can noticeably affect valve operation. Equalizer lines should always be piped in such a manner that they will not collect oil. Keeping the TEV power head on top (above the inlet an outlet connections) is also a good idea, particularly with internally equalized valves.
Internally equalized TEVs have a internal passageway from the outlet side of the valve to the underside of the power head for equalization purposes. As one can imagine, oil can collect at the outlet of the valve, particularly if it is feeding a bottom fed evaporator, and this oil can make its way to the power head if the TEV is upside down.
Of course, if the TEV is starving due to some other cause, refrigerant velocities in the evaporator are going to be lower, which will promote oil trapping in the evaporator and suction line. But then one needs to figure how the oil is getting into the equalizer line. If it is not due to poor equalizer piping or hot gas defrosts, a bad TEV pushrod seal might be a possibility. A bad seal could be the result of the TEV being overheated during installation.Prof Sporlan
-
26-04-2002, 03:03 AM #3
The last time I checked... oil was a liquid. Doesn't it transmit pressure OK? It is more viscous than vapor but that would only be a problem if there was a flow. There should be no significant flow in the equalizer line.
Prof., Are you saying that oil under the power head can contain cold refrigerant that will condense the power element charge, causing a situation similar to a cross ambient condition where the valve will not open? Wouldn't that be only a temporary situation until the refrigerant is gone? What seals the pushrods ?
-
26-04-2002, 02:33 PM #4Prof., Are you saying that oil under the power head can contain cold refrigerant that will condense the power element charge, causing a situation similar to a cross ambient condition where the valve will not open?
Wouldn't that be only a temporary situation until the refrigerant is gone?
What seals the pushrods ?Prof Sporlan
Similar Threads
-
MP66 & Compressor Overheating
By Intermez in forum Technical DiscussionsReplies: 111Last Post: 13-04-2010, 08:58 PM -
Interesting Problem
By NH3LVR in forum Industrial CompressorsReplies: 13Last Post: 12-08-2006, 10:27 PM -
Venturi for oil recovery in flooded system
By Friobernal in forum NH3Replies: 7Last Post: 11-08-2005, 09:20 PM -
Balanced port TEVs
By Prof Sporlan in forum FundamentalsReplies: 22Last Post: 25-02-2002, 03:43 PM