    Scroll oil return port



    Hi all
    We are currently building 4 scroll condensing units to include oil seps,cpr etc. We have noiticed that the oil return port from the sep on to the compressor is lower than the compressor oil site glass, on semi's the oil return is always above the oil site glass, should we be wooried about anything?

    Units are 7.5 Hp Copeland scrolls.

    regards
    LRAC



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Scroll oil return port

    Quote Originally Posted by LRAC View Post
    Hi all
    We are currently building 4 scroll condensing units to include oil seps,cpr etc. We have noiticed that the oil return port from the sep on to the compressor is lower than the compressor oil site glass, on semi's the oil return is always above the oil site glass, should we be wooried about anything?

    Units are 7.5 Hp Copeland scrolls.

    regards
    LRAC
    No need to worry. The oil on scrolls is injected in at high pressure direct from a small oil header that is fed from your sep and is controled by an oil management system that managers the level of the oil in the comp.

    Cheers taz.

  3. #3
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    193
    Rep Power
    20

    Re: Scroll oil return port

    look at henry optronic regulators we've been using them for 4 years and had no problems with either high or low pressure oil return this leaves the fill port free for initial fill and future draining. remember though if using low pressure return take out the orifice from the feed port before fitting.