    Why don't A/Cs have gas pressure gauge
    I was wondering. Why don't Arir Condition Units (outside or inside unit) have a gas pressure gauge?
    I read on various forums, how their A/C stop heating/cooling and then it turned out, that the gas leaked out.
    Why don't A/C have such a gauge so the user would see exactly the gas pressure in the system (like natural gas central heating system, which has water pressure gauge)?
    rbartlett's Avatar
    rbartlett Guest
    Re: Why don't A/Cs have gas pressure gauge
    now that inverters are becoming the norm a gauge reading isn't any use
    cheers
    richard
    Nov 2005
    Liverpool
    49
    56
    ...Also, fixed speed (Non Inverter) units tend to be more common at the Budget end of the market so cost is everything. If it works without, they won't fit it!
    DM
    Slovenia, EU
    49
    30
    Quote Originally Posted by rbartlett View Post
    cheers
    richard
    Why is that so?
    If there's a gas leak, I'd still like to know about it, or at least some sort of error code being displayed by the internal unit.
    11,025
    As a gauge costs money then they will not be fitted as standard.
    Slovenia, EU
    49
    30
    I thought as much that that is the only reason.
    Oct 2006
    1,843
    21
    Quote Originally Posted by AndY1 View Post
    Money is one main reason but the other is
    "a little information is dangerous" The preassure gauge does not indicate refrigerant contents. It relates to the pressure and temp of the refrigerant at that moment. A gauge would not indicate loss of gas and would alter dependent on ambient temps. A customer with no experience would not be expected to understand that.
    Cheers taz.
    Nov 2006
    Merlion Home
    35
    A sight-glass put into the system will indicate the refrigerant condition. But it will add to the cost.
    There is other sign of gas leak like ice formed on evaporator coil (provided it is not due to clogged coil).
    Mar 2006
    Merate (LC) - Italy
    2,549
    I agree, money is everything. If you assure me that all your splits will go through me, I'll install whatever you like in them, at a higher price than market.
    Since nobody will buy from you at those prices, I won't bother.
    Jun 2001
    N.Ireland
    1,630
    Splits probably don't need gauges
    Better to measure the liquid line suction line and discharge temperature
    If you service splits this way you will not reduce there performance everytime you remove your gauges
    Kind Regards Andy