    internal piping



    Anybody got any pdf format of piping schematic for a cassette fcu R407c?
    Daikin vrv heat recovery.

    Jase



  2. #2
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: internal piping

    Jase if you visit the Daikin website and put in your e-mail you can then download a good selection of manuals. If your stuck u can private message me and i'll send you the one you need. Can i ask why you would need the diagram as there is not alot to see other than a coil with expansion valve, couple of filters and three thermistors.

  3. #3
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: internal piping

    Just out of a matter of interest really!
    Have a problem unit which is not cooling or heating. Suspect linear expansion valve @ fault but may possibly be a blockage of some sort. Hence my curiosity at a peek @ a schamatic

    Regards
    Jase

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: internal piping

    As Puddleboy said Jase, log on to the Daikin website, there is a wealth of manuals on that site; well worth it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: internal piping

    Hello Jase,

    Attached is the service manual for the VRV K series heat recovery systems.
    Indoor unit not heating or cooling. First check the EEV is not letting by, set to cooling mode with a high set point (say 32*C) and check the liquid pipe temp. It chould be more or less the same as the gas pipe. If its much lower then the unit may have entered freeze protection at which point the stat is forced off. If the EEV is OK then check the suction gas solenoid valve coil in the BS BOX. Does it have 230v ac to energise the valve or may be the coil is burnt out.
    There may be a blockage in the liquid pipe (if its 1/4") but unlikely if the unit has cooled before.

    Have fun.

    Obi Wan

  6. #6
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: internal piping

    okay dokay