Are you sure in this values
Speaking about your scheme is the venting line from siphon receiver to condenser really connected in that way
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
01-11-2006, 05:25 AM #2
Re: NH3 thermosiphon oil cooler
Hi Josip,
Thnak you! Your question is very important, I don't why, but the values are measured a few days ago, I think except some measured errer they should be correct.
Another problem is that the fulid out of the condenser has a 9℃ sub-cooling! There must be something wrong with the system!
Best regards
cygbob
-
01-11-2006, 02:49 PM #3
Re: NH3 thermosiphon oil cooler
What is the diameter of the vent line pipe? And, what are the dimensions of the pilot receiver?
-
03-11-2006, 01:18 AM #4
-
03-11-2006, 02:00 AM #5
Re: NH3 thermosiphon oil cooler
Based on a very quick review, the pipe sizes you have listed appear to be OK. The pilot receiver volume also appears sufficient.
In your last drawing you stated the liquid drain temperature from the condenser is 26.6 C (79.9 F), but after the liquid flows through the receiver the liquid ammonia temperature suddenly increases to 34.4 C (93.9 F).
What is the condensing pressure?
Can you provide a drawing of the internals of the receiver also please?
-
03-11-2006, 06:44 AM #6
-
01-11-2006, 02:53 PM #7
Re: NH3 thermosiphon oil cooler
You have a lot of subcooling! This may be affecting the continuous flow needed to keep the Thermosyphon vessel filled.
I recently ran into this problem. We had multiple condensers and plenty of capacity, but high head pressure and high subcooling. The piping for the equalizing line was questionable.
We valved off the inlet to one of the condensers and saw no major improvement. We started the purger (which was not piped well) and the head came down and everything worked fine.
-
01-11-2006, 10:44 PM #8
Re: NH3 thermosiphon oil cooler
Hi Cybob
I will go for the old favorites
1. liquid supply trapped going to the oil cooler
2.Incorrectly sized wet return riser from the oil cooler to the condenser
3. Oil trapped in the refrigerant shell.
If you check this and rule them out it will help you reach a valid conclusion
Kind Regards AndyIf you can't fix it leave it that no one else will:rolleyes: