    Re: NH3 thermosiphon oil cooler

    Hi, cygbob

    Quote Originally Posted by cygbob
    300KW, tube counts:717, circulation ratio:3:1, oil inlet/outlet temperature:80/40 Deg C, ammonia: 38/39 Deg C.
    Here you have dT=1-2 C

    Quote Originally Posted by cygbob
    251KW, oil:87.7/49, ammonia:33.3/35.4,
    And here you have dT= 14-16 C

    Are you sure in this values

    Speaking about your scheme is the venting line from siphon receiver to condenser really connected in that way

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  2. #2
    Join Date
    Aug 2006
    Location
    CHINA
    Posts
    29
    Rep Power
    0

    Re: NH3 thermosiphon oil cooler

    Quote Originally Posted by Josip View Post
    Hi, cygbob



    Here you have dT=1-2 C



    And here you have dT= 14-16 C

    Are you sure in this values

    Speaking about your scheme is the venting line from siphon receiver to condenser really connected in that way

    Best regards, Josip
    Hi Josip,
    Thnak you! Your question is very important, I don't why, but the values are measured a few days ago, I think except some measured errer they should be correct.

    Another problem is that the fulid out of the condenser has a 9℃ sub-cooling! There must be something wrong with the system!

    Best regards
    cygbob

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: NH3 thermosiphon oil cooler

    What is the diameter of the vent line pipe? And, what are the dimensions of the pilot receiver?

  4. #4
    Join Date
    Aug 2006
    Location
    CHINA
    Posts
    29
    Rep Power
    0

    Re: NH3 thermosiphon oil cooler

    Quote Originally Posted by US Iceman View Post
    What is the diameter of the vent line pipe? And, what are the dimensions of the pilot receiver?
    the diameter of the vent line pipe is DN100,the pilot receiver dimension is about 1 m3

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: NH3 thermosiphon oil cooler

    Based on a very quick review, the pipe sizes you have listed appear to be OK. The pilot receiver volume also appears sufficient.

    In your last drawing you stated the liquid drain temperature from the condenser is 26.6 C (79.9 F), but after the liquid flows through the receiver the liquid ammonia temperature suddenly increases to 34.4 C (93.9 F).

    What is the condensing pressure?

    Can you provide a drawing of the internals of the receiver also please?

  6. #6
    Join Date
    Aug 2006
    Location
    CHINA
    Posts
    29
    Rep Power
    0

    Smile Re: NH3 thermosiphon oil cooler

    Quote Originally Posted by US Iceman View Post
    Based on a very quick review, the pipe sizes you have listed appear to be OK. The pilot receiver volume also appears sufficient.

    In your last drawing you stated the liquid drain temperature from the condenser is 26.6 C (79.9 F), but after the liquid flows through the receiver the liquid ammonia temperature suddenly increases to 34.4 C (93.9 F).

    What is the condensing pressure?

    Can you provide a drawing of the internals of the receiver also please?

    ok! the condensing pressure is 12.7barg. the delivery gauge is about 35.5 ℃. the receiver is empty!
    but ,I don't understand why the dT is so large!

    best regarsds
    cygbob

  7. #7
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: NH3 thermosiphon oil cooler

    You have a lot of subcooling! This may be affecting the continuous flow needed to keep the Thermosyphon vessel filled.
    I recently ran into this problem. We had multiple condensers and plenty of capacity, but high head pressure and high subcooling. The piping for the equalizing line was questionable.
    We valved off the inlet to one of the condensers and saw no major improvement. We started the purger (which was not piped well) and the head came down and everything worked fine.

  8. #8
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: NH3 thermosiphon oil cooler

    Hi Cybob

    I will go for the old favorites

    1. liquid supply trapped going to the oil cooler

    2.Incorrectly sized wet return riser from the oil cooler to the condenser

    3. Oil trapped in the refrigerant shell.


    If you check this and rule them out it will help you reach a valid conclusion

    Kind Regards Andy