Thread: Water Chiller

  1. #1
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Smile Water Chiller



    Hi everybody,

    I am asked to design a water chiller to cool water with temp. of 40°C which flows constantly with low flow rate.
    I think that with one chiller this would be a problem because of high entering temp.
    I want to use two chillers with one heat exchanger in between, i.e. cold water from the first chiller goes into a plate heat exchanger then cools the 40°C water to 15°C then this cooled water enters the second chiller.
    Any comment will be appreciated.

    Cheers.


    Even Einstein Asked Questions

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Water Chiller

    What is the expected leaving water temperature?

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Water Chiller

    Quote Originally Posted by lana View Post
    Hi everybody,

    I am asked to design a water chiller to cool water with temp. of 40°C which flows constantly with low flow rate.
    I think that with one chiller this would be a problem because of high entering temp.
    I want to use two chillers with one heat exchanger in between, i.e. cold water from the first chiller goes into a plate heat exchanger then cools the 40°C water to 15°C then this cooled water enters the second chiller.
    Any comment will be appreciated.

    Cheers.

    Flow rate, voluum of water and end temp are all critical to working out the size you need.
    They way you explain would work, taking the temp down in stages. one system correctly sized would do it alsoit literaly is horses for courses.

    Cheers taz.

  4. #4
    Join Date
    Feb 2006
    Location
    Mumbai
    Posts
    49
    Rep Power
    0

    Re: Water Chiller

    Hi Lana,

    If your assuming that 40deg C is Dry bulb temperature. If you can get 30 to 32 deg C of wet bulb temperature then it would be a better option to go for a cooling tower rather than a chiller !

    Regards

    Vijay Kumar
    HVAC Engineer
    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Water Chiller

    Why you think an entering temperature of 40°C with a chiller in a counterflow setup will give problems?
    The only thing the warm entering water will do is raise the SH, not necessarily the evaporating pressure.
    NoNickName is the best person to judge this.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Water Chiller

    Quote Originally Posted by Peter_1 View Post
    Why you think an entering temperature of 40°C with a chiller in a counterflow setup will give problems?
    The only thing the warm entering water will do is raise the SH, not necessarily the evaporating pressure.
    NoNickName is the best person to judge this.
    I would say to use MOP TXV (or even better: EXV) to limit the SH and numerous baffles in the s&t evaporator.
    Nothing is said, though, about the required leaving water temperature.

  7. #7
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Unhappy Re: Water Chiller

    Thank you all.
    The required water temp. is 5 or 7°C and the flow rate is 2 lit/min.
    There is no way that a cooling tower could be used because of ambient conditions.
    I have an experience with an air cooler which was supposed to cool 70°C steam. There the suction pressure went up (also the SH) and basically there was no way that the TEV could be adjusted to get the required capacity .
    Here I will use plate heat exchangers both for evaporators and the middle HX.

    Cheers.
    Even Einstein Asked Questions

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Water Chiller

    40° to 5°? What is the application, just for curiosity.

  9. #9
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Water Chiller

    Quote Originally Posted by lana View Post
    Thank you all.
    The required water temp. is 5 or 7°C and the flow rate is 2 lit/min.
    There is no way that a cooling tower could be used because of ambient conditions.
    I have an experience with an air cooler which was supposed to cool 70°C steam. There the suction pressure went up (also the SH) and basically there was no way that the TEV could be adjusted to get the required capacity .
    Here I will use plate heat exchangers both for evaporators and the middle HX.

    Cheers.
    Are you using the water to add to flour to mix bread by chance.

    Cheers taz.

  10. #10
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Water Chiller

    Hi there,

    The cold water is used to cool some kind of high temp. gas in the chamber jacket.

    Thanks
    Even Einstein Asked Questions

  11. #11
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Water Chiller

    Quote Originally Posted by lana View Post
    Hi there,

    The cold water is used to cool some kind of high temp. gas in the chamber jacket.

    Thanks
    In that case, why not cool the gas directly with the primary circuit. Cut out the middle man
    It would be more efficient to cool the gas directly with the primary system.

    Cheers taz.

  12. #12
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Water Chiller

    You can design a unit for 40 dC inlet, but you need to careefully watch the compresssor inlet temperature and it's limits. You can use a run-around loopto temper the water temp entering the chiller. Or use a secondary process loop and a primary chiller loop with a mixing tank to temper the return to the chiler.

    Personally, I'd go with the two pump and mixing tank approach to keep it in a standard chiller.

    Ken

  13. #13
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Water Chiller

    Hi TXiceman (Ken),


    Thank you.
    What I am going to do is :

    Use first chiller to cool 40°C to 15°C by using a Plate heat exchanger therefore 40°C water will not enter the chiller evaporator.
    Then the second chiller will cool the 15°C water to 7°C.
    Because of very low flow rate I don't think that water tank is necessary.

    Regards
    Even Einstein Asked Questions

  14. #14
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Water Chiller

    You will need some sort of expansion tank for the closed loop system. I like to keep the loop closed or sealed under a low pressure nitrogen pad to keep out contaminents. You will need some inhibitors in the water to control corrision and letting it breath as in an open loop will deplete the inhibitors sooner.

    The expansion tank can be either a simple sealed tank or a bladder tank.

    You can do it in one loop system with a hot/cold divided mixing tank and separate pumps for the process flow and for the chiller flow. By using the mixing taank, you can keep the hot water off the chiller.

    Ken

  15. #15
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Smile Re: Water Chiller

    Thank you TXIceman. Most helpful.
    Cheers
    Even Einstein Asked Questions

  16. #16
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Water Chiller

    Lana.

    You may already have this contact,
    SWEP They make plate exchangers just as Alfa Laval etc. I'm not allowed to post the URL here because I'm still a rookie! But you'll know how to do a search ...i'm sure?

    They will let you have selection software for plate exchangers. Which I have used for many years ..much better than the old fashioned shell and tube.

  17. #17
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Water Chiller

    Quote Originally Posted by lana View Post
    Hi everybody,

    I am asked to design a water chiller to cool water with temp. of 40°C which flows constantly with low flow rate.
    I think that with one chiller this would be a problem because of high entering temp.
    I want to use two chillers with one heat exchanger in between, i.e. cold water from the first chiller goes into a plate heat exchanger then cools the 40°C water to 15°C then this cooled water enters the second chiller.
    Any comment will be appreciated.

    Cheers.
    Hi Lana

    Just an idea and i did not make any calculation for it. what about you using Package unit with DX coil with a certain capacity with all return air and then using the cooled air from this Package to cool the water from 40°C to 5°C. that means using finned-tube heat exchanger in which the tube side is the hot water of 40°C and the cold side is the supplied air from the package unit over the finned-tube. By this u strike, avoid abnormal raising in chiller suction temperature and energy saving of using all return air. I wish this idea is reseaonble for being used in ur project

    Cheers

  18. #18
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Water Chiller

    Quote Originally Posted by mohamed khamis View Post
    Hi Lana

    Just an idea and i did not make any calculation for it. what about you using Package unit with DX coil with a certain capacity with all return air and then using the cooled air from this Package to cool the water from 40°C to 5°C. that means using finned-tube heat exchanger in which the tube side is the hot water of 40°C and the cold side is the supplied air from the package unit over the finned-tube. By this u strike, avoid abnormal raising in chiller suction temperature and energy saving of using all return air. I wish this idea is reseaonble for being used in ur project

    Cheers
    oh sorry i discover a mistake in the idea. It should be divided into stage, the first one as a formentioned by using package unit and the second stage by using chiller. Because of the minimum supply temperature will be exited from package unit may be around 10°C to 12°C and this makes the water outlet temperature form the finned-tube heat exchanger of 15°C to 17°C. therefore, this cold water will complete its cycle to go to a chiller of Tev of 2°C to discharge chilled water of 5 or 7°C as u need. This is Just an idea

    cheers

  19. #19
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Water Chiller

    Thanks everybody,

    I have proposed the two chiller units which has been proved but there is no contract for the job yet.
    Everything takes ages to complete.

    Cheers
    Even Einstein Asked Questions

  20. #20
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Water Chiller

    That's the way of contracting .... loads of design and probabilities ...then the wait for the order .....and then more waiting and then more re arranging and so it goes on. Why do we do this?

  21. #21
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Water Chiller

    TXICEMAN.

    I like to keep the loop closed or sealed under a low pressure nitrogen pad to keep out contaminents. You will need some inhibitors in the water to Control corrision and letting it breath as in an open loop will deplete the inhibitors sooner.


    If you blanket with nitrogen then surely there will be no need for the inhibitor as there will be no oxidation occuring?