Results 1 to 2 of 2
  1. #1
    Join Date
    Oct 2006
    Location
    Romania
    Age
    52
    Posts
    13
    Rep Power
    0

    suction and discharge head for parallel compounding compressors



    Does anybody know a rule for calculating the diameter of suction and discharge head Copeland, Frascold so on compressors?

    Thank you!



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: suction and discharge head for parallel compounding compressors

    The diameter for the main header is not that important -take full capacity - but what's extremely important is how you connect the different compressors to that common header.

    Suction: make that all will return to the compressors.
    Discharge: make that header is lower then the compressors to avoid oil or liquid flowing back during stand-still.

    Bitzer has a very good bulletin about this. www.bitzer.de
    Read this once

    You're speaking about parallel compounding. For me parallel is something complete different as a compound setup.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.