    Oct 2006
    UK, London
    11
    Post flow control - NH3 recirculated evaporator
    Other than the usual manual balancing valve, are there any other type of (perhaps automatic) liquid flow control or expansion devices that can be used to control ammonia flow rate of forced recirculation (pump) evaporator ?.
    Simon
    Aug 2005
    5,302
    Re: flow control - NH3 recirculated evaporator
    Simon,
    Here are several links for the products I am aware of:
    http://www.parker.com/rs/41-10C.pdf
    http://www.parker.com/rs/41-15A.pdf
    I hope that helps.
    Best Regards,
    US Iceman
    Jan 2006
    Valrico, Florida
    509
    Hansen has motorized valve, and Parker/Seimens also has a valve for liquid feeds for NH3, 2 of our plants have these and they seem to work very well. Oh and Danfoss has one also
    Mar 2006
    Frederikssund
    49
    hi
    aDanfoss CVQ pilot on PM vavle using EKC 361 or 366 as regulator
    see www.danfoss.com
    this is working Ok
    Aug 2005
    5,302
    Hi there,
    Quote Originally Posted by nh3wizard
    Hansen has motorized valve, and Parker/Seimens also has a valve for liquid feeds for NH3...
    Can you post some links to these please? I'm not sure I follow how a motorized valve would be used or controlled for a liquid feed/balancing valve for a recirc. evaporator.
    Jan 2006
    Valrico, Florida
    509
    Hi there,
    These are used for the liquid feeds to the recircs. Ill look for the links and post.